I have a A/B PLC5/80B processor in a remote plant (1000 miles away). This processor has channel 1A connected to the local DH+ network, which has SLC5/04s and PC on it. Channel 3A is connected up to the plant's ethernet network. Using RSLinx and our WAN, I am able to connect up to the PLC5/80. Is there a way for me to bridge through the 5/80 and get to the other processors on the DH+ network?
I am doing this at another plant using a 1756-ENBT & a 1756-DHRIO cards, but there I am not bridging a PLC.
Users are so accustomed now to bridging through ControlLogix that they often forget you can't do that with a PLC-5.
No, you cannot bridge between any of the PLC-5 network channels.
Probably the easiest way to get this done is to install RSLinx Gateway on the PC that connects to your DH+ network. RSLinx Gateway will allow you to use that local 1784-KTX or PKTX card on the remote machine over a TCP connection.
Now that raises an interesting question...
Would connecting a Net-ENI to one of the SLC-5/04 serial ports and then connecting the other side of the ENI to the plant Ethernet network let you bridge through the SLC-5/04 to the other 5/04s on the DH+?
If so, is this a reliable solution?
Thanks,
(8{)} ( .)
Thanks Ken. That is what I thought. I do not need to get into their network very often, so when I do I will make the trip. They will not spend money to give me access from afar, but they will spend money for me to fly out and visit for a week.
The only step to take now is to find a good restaurant near the plant with cute waitresses and good coffee.
Hey Everyone, I have an AB PLC 5/80B processor that has a comms fault on Rack 14 which is a Flex ASB adapter the module has a flashing green...
10,962
I am using the following formula and I am getting error, Invalid Expression - too many closing parenthesis. when i copy the formula to notepad or...
156
Preface: Kinda long, so I made section titles Intro: I just want to see if anyone here has seen anything similar. A PLC5-40 series C enhanced...
373
Hi, can anyone help me get a pdf file for this RSP files. They are from a PLC5. Thanks
522