PLC5 rack addressing
I think you're right about it being done to make it easier to tell RIO from DH+. I never bothered to follow that. It didn't actually matter as long as the wiring for all nodes matched.
Always hated the modules that flipped the numbering. I had a general rule for both networks of blue to #1. For most modules #1 was on top so at a glance you could verify. But some modules reversed the connection so #1 was on bottom. Hated that.
OG
"The Highway is Clear" was a phrase we used to remember to use the Clear conductor for DH+ pin 1, and Blue for RIO pin 1. If you are consistent and have a lot of these networks installed, it can be helpful.
What was even more helpful was a cable label that indicated the type of comms along with a reference like rack number (RIO) or PLC name or node number (DH+). ie "RIO RACK 3", "DH+ NODE 6"
Cable labeling for comms cables ? what a luxury you had !
Many installations I have worked on had no such ident attached, simply meaning it was either I/O or comms.
The devices the cable connected to were software configurable, and you had no idea from/to where it was connected.
Many hours spent "buzzing" cables out, simply because ident was not attached, and of course that meant disconnection and downtime to the systems.
Hi, i need help, i have a plc 5/80c 1.5 and the i/o config is: Local chassis (4 slots) onnly the processor and also 4 chassis each (16 slots)...
1,474
My goal is to get an analog signal from a SLC-500 remote rack back to a PLC-5 main rack. Is this possible? If so, I may need some help. I've set...
1,771
Hello, I have a potential project and I am rusty in communication skills. The project will consist of a Control Logix platform with an existing...
17
6,352
Curious if this is possible. I am working on a PLC5 to CLX conversion. Due to panel space limitations and time I need to replace a small PLC5...
3,502
I am looking for a bullet proof UPS that can handle temps up to 60 deg C. This is a remote rack at a pumping station. When power is lost, we loose...
3,550