PLC5 to Controllogix communication over RIO?
Paul351W
Mar 2008
Northern Illinois
154
I have an installation with a PLC5 system controlling a test cell, and I want to add a Controllogix rack with high speed analog I/O cards to do high speed pressure controls. I want to be able to request pressures with the PLC5 from the Panelview (1400e) in a "manual" mode, then accept commands through the high speed analog cards in "automatic" mode.
Can I use the existing RIO network in the test cell to communicate commands and status bits back and forth between the two processors? The other installations I have done with this sort of setup used all digital I/O between the two controllers, and switching relays to swap the pressure command outputs.
With the existing Remote I/O system, the PLC-5 is the Scanner and the PanelView 1400e (and, I assume, remote I/O racks of some sort) are Adapters.
The standard 1756-DHRIO module cannot be an Adapter on RIO, only a scanner. To use it to interface with the PLC-5, you would need an available PLC-5 channel that can be placed in Adapter mode and dedicated to this purpose.
You could also do DH+ messaging (or Ethernet or serial) between the ControlLogix and the PLC-5, but of course this is generally slower and less predictable.
The new 1756-RIO module can be configured as an Adapter. You could put it in the ControlLogix chassis, add it to the PLC-5 scanlist, and use both discrete and block-transfer features to transfer data between the controllers.
Just to clarify this statement: You MUST have ControlLogix Processor in ControlLogix chassis with RIO module to act as an Adapter for PLC5 processor.
1756-RIO does not work without a ControlLogix controller
The CLX chassis will have a processor in it, that is what will be running the pressure control. The PLC5 would run the rest of the test cell as it has, and just communicate commands/status bits to and from the CLX processor.
It sounds like the 1756-RIO module might do what I need. I want to tie into the existing RIO structure in the cell and use that to communicate between processors instead of adding a separate dedicated communication link if at all possible.
In one of my project, end-user wants to connect Controllogix 1756 IO's with PLC 5/40E controller on DH+ protocol. 1756 DHRIO card is installed in...
6,738
Hello everybody, I need help to solve the following problem. Our client has maxed out the addressing space in their PLC-5 ControlNet network. The...
2,445
Hello, I'm starting in the PLC world, mostly doing troubleshooting and little changes to programs for the last year and a half, also have done a...
3,631
Hello, I am currently converting a project from PLC5 to ControlLogix. I have migrated the program from Logix5 to Logix5000 and any Block Transfer...
3,357
Hello, Today I am trying to figure out the best way to write from controllogix to a plc5 only on change. The situation: - Migrated a Winview...
2,121