PLC's, power supplies, and wireing

JOLTRON said:
What do you mean 0 to -24vdc??? I don't understand how you can get -24 volts.

Take any two batteries of any equal voltage. Wire them in series additive. In the series connection between the two hook up a test lead. Read to the opposite terminal of each battery. You will get + X volts on one and - X volts on the other.

The series connection between the two batteries could be used as a common.

In the days of tube electronics these were called B+ and B-

Dan Bentler
 
keithkyll said:
Sounds like more of a trick question than anything else. Two 24DC supplies, but one of them has + as the common. That's the only way you could get 48DC on the input.
PLC1 has relay output and soucing the -. +24 is wired to common return.
PLC2 has sinking inputs. -24DC is wired to common return (shared between the 2 supplies), and +24DC is wired to input common.

Does anybody tie +24 to ground? I don't think so.

You would be surprised! I have seen lots of Japanese machinery that has all the +24 tied to ground! ...and their drawings are
icon12.gif
backwards
icon10.gif
 
Last edited:

Similar Topics

Some PLC manufacturers sell power supplies that attach to the left of the PLC CPU modules (see controllogix and automation direct click's PLC)...
Replies
7
Views
2,213
Hello everyone, I have a PLC question, in regards to using several external 24 VDC power supplies, from different machines ! I only have (2)...
Replies
4
Views
3,547
Here is a newbie question. Are DC power supplies used for any reason in the industries that use PLCs? This is not including any PLCs themselves...
Replies
2
Views
3,735
Hello..I am new to Plc.I have Mitsubishi Melsec Fx3Ga-40MR PLC controlling a machine for packing powder.Currently the Plc has issue which power...
Replies
3
Views
143
Hello gentlemen, Im working on a small project on TIA Portal, about establishing a Modbus TCP connection between my ET200SP plc and a socomec...
Replies
12
Views
310
Back
Top Bottom