External 24 VDC power supplies for PLC inputs.
PLCrickster
Nov 2016
Illinois
Hello everyone, I have a PLC question, in regards to using several external 24 VDC power supplies, from different machines ! I only have (2) commons on my PLC inputs, but I need (1) more common. Can I use any -24 VDC common or does it have to be from that specific power supply ? Can my PLC 24 VDC inputs come from any external source, without that sources -24 VDC common ?
The input is an LED and a series resistor. The LED is inside an optoisolator. Treat it like a low current lamp.
All 24DC supplies need to have their -24 sides tied to each other and the PLC common.
If not, then you'll need to add more input cards.
Are the (2) commons you have now isolated?
You can common the -24vdc s of all the power supplies together. Such is the case if they bond to ground. This would insure your inputs would work.
I have (2) isolated commons on my inputs that I would tie the (2) separate power supplies -24 VDC too, but I have a (3rd) power supply to deal with. All (3) power supplies are exactly the same, does it matter if their isolated, or can I tie all my -24 VDC commons together, and not worry about isolation ?
If you are using any power supply to drive PLC inputs the common from that Power Supply must be connected to the common on the PLC input card.
Doesnt matter how many power supplies or what brand/type.
The easiest thing and most common approach is to connect all the input card commons and Input Power supply commons together.
Set up a few jumpered terminal blocks closest to the Input card and pull all your commons to them.
You dont need to isolate the input groups unless you have a SPECIFIC reason to do so.
I have a few questions about Studio5000. 1. Why is my RA folder so big? its well over 100 GB. 2. How do you delete versions or extra files...
279
I am trying to enable an external alarm via computer speakers for Factory Talk Network Distributed Edition. I am using Alarm and Events setup. I...
177
Good evening all! I hope you folks are doing alright today, as I've got a situation that I believe I've come up with a solution to but I wanted to...
448
As the title says, I'm trying to figure out a way to import and export recipe files from an external CF card to a USB drive and vice versa. I've...
497
Hi All, I'm using Studio 5000 ver 30 to modify existing logic that has PID, and I want to be able to use an external/remote source as a setpoint...
639