Please check my pid parameters.
Rahul3005
Dec 2017
Mumbai
34
Dear SIR,
In one of the scenario's, I have to control VFD Frequency (4-20 mA) , with Oxygen Analyser. (4-20 mA).
I have Configured PID Parameters as such.
Please check whether PID parameters are configured properly or not.
I have used SLC 5/03 and RSview32.
Generally in PID , CV is used for controlling Analog O/P , But in my case i have used Scaled ERROR word for controlling.
I dont know whether it's correct or not.
It's my first time tuning a PID loop.
Please Apologise if any mistakes or error .
Thank you.
Hi,and welcome to the forum
Just taking a guess--use your AI from the O2 analyzer and scale it in the PV in the PID as 4000-20000 and then whatever the range is on the analyzer. Say, 200-600 if it's in ppm.
The control variable will be 0-100 in the PID. So the output from the PID (in percent) will give you milliamps to the drive for the motor. Again, just a guess. Cardosocea is right, you need to post more info. I use a scaling block in FBD to scale most of my loops. Don't forget the free running update timer for the PID. Good luck
I had it easy. I usually had known good numbers to punch in for P and I to start w/.
When I didn't, I was usually hosed.
I find it helps if you slow the pid solve rate way down to start.
Integral windup:
Best way I can explain this.
I figured out how I could drive my rental car w/o using the gas pedal.
Oldsmobile Achieva.
Neutral wouldn't cancel the cruise control.
I could basically set the cruize control at 30- 70 and use the shift nob as the gas pedal.
Well, after doing this for most of the trip, I was at a red light w/ the car in neutral.
Light turned green, and the car acted like I floored it and went to red line. Nearly rear ended the car in front of me (which is hard to do w/ an Achieva).
I think this is integral windup.
Or if calculus makes more sense to you, I think it is the area under the curve.
Please find the attached file
I have attached pdf file of my ladder.
Somehow i was not able to attach my original backup , it was saying as invalid.
Please guide me.
Thankyou
Hey guys, I recently visited an existing water plant that's running a Scadapack32 with ClearScada for the HMI. I've been looking through the...
1,472
Hi Guys, Just installed WinCC V6.2 +SP2 on my laptop to make some modifications to an existing project. When I attempt to open the file I the...
14,162
Hi, I would like to run this scenario by you guys. I already have a licence for RSLogix 500, so I am limited to micrologix and SLC 500. I don't...
24
6,697
please help me . I have to make this ladder diagram and I can’t figure it out :(
374