Dear All experts,
The system:
I am having AB PLC to operate and control coal handling plant with many conveyors, flapgates, vibrating feeders etc.,
Power supply:
All I/O's are of 24Vdc...For Inputs +24 V DC gets distributed to Input devices via fuses (200ma each for each input)(like start Push button, Limit switches, Pullcord and beltsway....)
-24V DC Negative is grounded at panel.
The Problem:
Suppose one wire gets grounded at beltsway switch no.5 (for a single conveyor there may be 10 such switches connected in series and All together constitute a single input to PLC)....Fuse should blow up BUT NOT HAPPENING.
But if another wire of say Pullcord no.10 gets grounded We are facing a safety related problem because operation of Pullcord no 1 to pullcord 9 will not result any change in PLC INPUT BECAUSE +24V DC is available at Pullcord 10 due to ground.
My Attempt:
I tried to measure current flowing thru that particular fuse (where there is a ground) and found it is less that 100ma...
PLC panel is about 1000m far from the I/O.
Any suggestions??
The system:
I am having AB PLC to operate and control coal handling plant with many conveyors, flapgates, vibrating feeders etc.,
Power supply:
All I/O's are of 24Vdc...For Inputs +24 V DC gets distributed to Input devices via fuses (200ma each for each input)(like start Push button, Limit switches, Pullcord and beltsway....)
-24V DC Negative is grounded at panel.
The Problem:
Suppose one wire gets grounded at beltsway switch no.5 (for a single conveyor there may be 10 such switches connected in series and All together constitute a single input to PLC)....Fuse should blow up BUT NOT HAPPENING.
But if another wire of say Pullcord no.10 gets grounded We are facing a safety related problem because operation of Pullcord no 1 to pullcord 9 will not result any change in PLC INPUT BECAUSE +24V DC is available at Pullcord 10 due to ground.
My Attempt:
I tried to measure current flowing thru that particular fuse (where there is a ground) and found it is less that 100ma...
PLC panel is about 1000m far from the I/O.
Any suggestions??