WAIT! In you picture PRO3.jpg, on Rung 59 it appears that the F118 Counter has an EV0 (Elapsed Counter Value) = 9. Is that small blue "9" equal to the counter's value when you made the picture? The "9" also shows up on Rung 69 just above the "EV0". If that is the current value of EV0, then the counter is working, but it should not trigger the 50% Level Switch UNTIL it reaches "50". That is a long time to wait!
You could (for the purpose of faster testing) change the TMX timer on Rung 54 to a type "TMR" timer, with the set time still = "K10". That would speed the timer up by 10 times (0.01 time base instead of 0.1 seconds). Then you would only have to wait 5 seconds for the tank to hit 50%, instead of 50 seconds.
Another way to speed it up is simply to change the TMX 0 to a setting of "K1" or 0.1 seconds.
You could (for the purpose of faster testing) change the TMX timer on Rung 54 to a type "TMR" timer, with the set time still = "K10". That would speed the timer up by 10 times (0.01 time base instead of 0.1 seconds). Then you would only have to wait 5 seconds for the tank to hit 50%, instead of 50 seconds.
Another way to speed it up is simply to change the TMX 0 to a setting of "K1" or 0.1 seconds.