plz help,PD ctrl( PID in RSlogix5),it doesnt work with ouput%
vungtauso.com
Mar 2011
Viet nam
32
I want to display output in rsview32 by set bit PD14:0.OUT as picture bellow :
I have Setpoint value,Process Variable,but Error ?
thank you for reading.
From your screen shot your PID is in the manual mode.
For a more complete help you should post your .RSP file ( zip it first)
FYI : Again from the limited screen shot the rung with your PID instruction should be conditional, usually a timer. That's in the PLC5 world other controllers are different.
What ladder file is this in? Is it being called?
this is an small example use PID to control valve (0-100% ),it recieved sign from Level sensor (0-200 cm, 4-20 mA)
thank you so much
  • HuyTesLogix.zip
Appears to be something wrong with the zip file you posted I cannot not open it.
A second download of your zip file now I can open it.
The file in the zip is different then the screen shot one.
In the zipped file you should put a one second timer bit on the same rung as the PID this will match the configured update time of the PID instruction. See picture
You have the control action set to "PV-SP" ( direct acting) your process will have to exceed your setpoint for an output to start increasing.
In the file you first posted you had the "BTR" BTW" instruction set up properly.
In the new file they are not go back to the original setup.
Also see my picture above on how to trigger the PID instruction with the XIC timer done bit. The way you have it in the new posted file will not work.
I trying to make it work,in the first and second post it not work,I dont know why,I set up PID the same with some correct example in manual PLC5 but...
thank for your advise. i will try with this question
the driver setting indicates that you're running this in the EMULATOR ... sorry - that won't "do" PID ...
in simplest terms, the Emulator software will NOT execute/run the PID equation ... you need a real/hardware PLC-5 for the PID to work ...
Hi Can I get the programming software and data cable name for allen bredly servo drive which model is 2098-DSD-020x?
2,227
I need some assistance to any Siemens Gurus' who can help me convert the following from STL to Lad. I have tried all the old tricks I can...
4,323
Any body here to help me regarding S7-300
1,359
hey evry one i have this problem In the system with S5 CPU 927 it is work ok, but i try to run another four CPU 927 for backup but no one of the...
3,906
sir plz tell me how to interface servo motor with abb micrologoc 1400b plc plz give me detail of instruction and wht type driver may i use or tell...
2,528