Pneumatic Valve
dwpang
Aug 2012
singapore
68
Hi may I know where I can get pneumatic valves which can receive input signal from PLC and also give output signal back to PLC?
cause currently my pneumatic valves are only receiving input signals, and I forgot to on the air supply and the inability to read feedback signals cause some problems to the system.
thanks.
What pneumatic valves are you using at the moment?
Most pneumatic valves will have an option to add a sensor for feedback, but it all depends on the manufacturer.
I use Alpha-Laval for all of my valve needs, and these come with a number of options to give feedback to a PLC etc.
Mark
Hi for my pneumatic actuator i am using Air Torque.
There is also attached solenoid valve for electrical input, using AirTec Series KN-05 Standardized Valve, with an attached solenoid.
I think they do not have options to give feedback to PLC
Add a pressure switch to the main air supply. You can use the NPN output for a simple 'air is on' signal. You could also display incoming air pressure on the HMI.
There are many manufacturers that make this type of switch. This one is from Automation Direct.
The KN-05 doesn't have a feedback option. You wouldn't want that on the pilot valve anyway.
Air Torque has optional position switches. See the last photo on this page. It looks like an open/closed sensor.
Hello automation experts, I kindly ask your help about the pneumatic valve shown in the attached image. The valve is 3/2 which means it should...
2,939
Hello experts, There is a control loop with PID controller and pneumatic actuator that controls the position of the valve. Pneumatic actuator has...
2,262
Hello, i would like to control a pneumatic valve based on conductivity of the medium in the pipe. I want to receive OPEN and CLOSE feedback as...
1,404
Hi Gents, Please could someone assist me in understanding this piece of equipment as to how it works. Any feedback would be greatly appreciated...
3,941
Hello guys, I'm in a bit of a dilemma - not very clear on the operation the typical PID controller. Here's the issue: A client has a turbine...
3,804