Power Distribution Options - 150 Amps
tspisak
Aug 2005
Corning, NY
72
Does anyone know of a clever way to distribute 480 vac, three phase voltage for applications over 100 amps? I have a project where the customer wants to have a single point power disconnect of 150 amps for multiple cells. The power gets split out to power for transformer, automation, conveyor motors, and the PLC panel.
The wire size is too large coming out of the disconnect to fit in to the 30 amps fuse holders. May just have to put in an intermediate fuse allow the use of smaller gauge wire and just up-size the enclosure.
We use power distribution terminal blocks too (I prefer the IEC type but they are expensive). The problem is the wire size (#1 AWG) is too big to fit into a 30 amp fuse holder.
If you use the distribution blocks then why are you running a ~200 amp wire into a 30 amp fuse?
Unless he's trying to get away with not using PDPs, hoping to jump from the disconnect-to-holder-then-to-holder, etc. And that would not be good.
"May just have to put in an intermediate fuse allow the use of smaller gauge wire and just up-size the enclosure. "
Best fire the panel designer, spring for the PDPs, and make sure its in the quote for the next panel. Multiple wires coming out of the intermediate fuse holders will look poor to anyone used to dealing with power distribution. My customer's would reject it.
The order of the devices would be:
200 amp disconnect with 150 amps fuses
Power Distribution Terminal Block
(6) 30 amp - 3 phase fuse holders
The wire to handle to 150 amps into and out of the power distribution block is too big to fit into a 30 amp fuse holder.
Shouldn't the the wire be sized to match the 150 amps fuse that is protecting the wire downstream of the disconnect until the next fuse?
The power distribution block should a single connection to the inboard side and the outboard side should have multiple 30 amp wire connections. Sounds like you've got the wrong model there?
Per NEC 240.21 (B) you can use 1/0 AWG (150A)wire from your main disconnect to your power distribution blocks. then use 10AWG (30A) wire to your 30A fuse holders. The total length can not exceed 10 feet. The tap conductors can not extend beyond the the panel that your main disconnect is in.
TWS - Thanks! That is what I needed. I thought that you had to size ALL of the conductors for the fuse above the PDTB in case of a direct short to ground.
All of my power distribution is in the same cabinet so I am good to go.
Looking at installing point io, with a 1734-AENTR communications adapter and ten 1734-IT2L modules. In IAB it installs a 1734-EP24DC after every...
73
In our PLC, we've got a 24VDC (5 amp) power supply - it's a PULS cp5, which connects to a DIN rail. I need it to supply power to 8 x Druck...
1,151
We are working on a project that includes the requirement for us to provide a 400A 480vac distribution panel with breakers to supply the 3-phase...
4,465
Hello Guys, I have a question thats not directly related to PLCs, but for those of you who work or have worked in contental Europe (anywhere...
2,626
We have some issues with our main 1200A service that feeds part of our plant. It has ground fault interrupter relay which tripped four times since...
3,810