califflash
Member
Tspisak,
I do not have the NEC in front of me at the moment but you DO NOT have to size the wire of the individual taps to carry the full current allowed by the primary over current device. You do, however, have to size the branch protector that the tap feeds to protect the wire. For example you can tap off a 000 feed with 10 awg wire, with the appropriate device (ie: pdp), but that tap must connect to a branch protector rated at no more than 30 amps, or less depending on de-rating factors. This is quite common.
On a side note, if your fusing is located in one location, you may use a bus bar and terminal lugs to feed the individual branch protectors. The sum of the branch protector ratings cannot exceed the rating of the bus bar, lugs, or fusing. This is my preferred method because it cuts down on the number of wires, labels, and assembly time.
I do not have the NEC in front of me at the moment but you DO NOT have to size the wire of the individual taps to carry the full current allowed by the primary over current device. You do, however, have to size the branch protector that the tap feeds to protect the wire. For example you can tap off a 000 feed with 10 awg wire, with the appropriate device (ie: pdp), but that tap must connect to a branch protector rated at no more than 30 amps, or less depending on de-rating factors. This is quite common.
On a side note, if your fusing is located in one location, you may use a bus bar and terminal lugs to feed the individual branch protectors. The sum of the branch protector ratings cannot exceed the rating of the bus bar, lugs, or fusing. This is my preferred method because it cuts down on the number of wires, labels, and assembly time.