Power Factor Correction Capacitors
Timeismoney08
Jul 2012
United States
312
Hello,
I was just curious if a PF correction capacitor is ever used with a VFD install?
Have any of you ever needed to add a PF correction capacitor in any of your builds?
Thank you!
Out of pure interest, how were you 'bit'?
On one occasion, I was commissioning a panel with a handful of VFDs and a couple of servos. The servo motion would occasionally act erratic. After much time scratching heads and thinking that it was a tuning problem, I noticed the h/w designer had not designed in line reactors for the VFDs or Servos. I asked the electrician to rummage in their bone yard and install some in the new panel and the erratic behavior disappeared (or never again showed up).
Input reactors stop drive noise from contaminating the supply.
Output reactor reduce the noise on the motor cable and reduce the chance of crosstalk to other cables.
PFC is not needed with a VFD. With a large amount of VFD's in an industrial plant, you may need to look at a harmonic filter.
As stated above, input reactors mitigate some of the noise and harmonics that are sent on the line feeding the VFD. Output reactors are to smooth out the pulsed voltage that is created from the SCR's firing. They are also used to stop the reflected voltage spikes that are created with long leads from the VFD to the motor.
Folks, My boss say's he is paying a large fee due to Mostly inductive loads. He thinks it's because the guys come in and start up all the...
28
9,192
Hi, Is it possible to use Power Factor Correction in a residence having a 230 V single phase supply. Will power factor correction reduce the...
22
8,930
Hi all I know that this question is not related to plcs but would be much obliged if you could help. We have 360KVAr 400 Volt PFC Bank 6...
2,746
Unregistered
U
At the end of the day today I walked over to a panel that a co-worker was commissioning and noticed a buzzing in the panel. I traced it to the 40...
17
5,902
guest1
G
I am calculating power factor from samples of voltage and current. Calculation is done by multiplying voltage and current samples. What Im...
1,650