At the end of the day today I walked over to a panel that a co-worker was commissioning and noticed a buzzing in the panel. I traced it to the 40 HP motor starter which is used for a hydraulic pump.
REPLY Sounds like single phasing to me. BUT do any of the relays buzz normally??
The customer spec called for PF correction caps which I had never used before so we got a recommendaiton from
http://www.myronzucker.com/. The caps are wired after the starter.
REPLY OK in parallel with the motor.
The motor had been started earlier in the day to check rotation but now it was not turning. There were no blown fuses although the overload blew once.
REPLY Check rotation implies to me start for one sec or so to get it turning then shut it down - Especially if you gotta reverse rotation.
Can improprely sized capacitors (too small) cause this?
QUESTIONS
1. When they did phase rotation did they leave it running? Does anyone know how long it ran?
2. What were running amps?
3. What were starting amps?
4. You said the overload blew -- was it still blown when you found the buzzing?
5. How are the overloads sized and are they mags or thermals or a CT relay setup?
6. How many overloads are used?
7. Did you run motor after reset overloads and what happened??
8. Are there (or were) there any mechanical problems that overloaded the motor??
9. This is across the line starting and not VFD (sorry gotta ask)
10. Are you able to measure PF when the motor is running - are you getting what you want?
11. IF an overload tripped why did (IF that is the case) the main contactor remain shut thus single phasing the motor??
My guess is that when starting the caps and the motor windings both draw current. IF the caps are undersized then they would draw less than if they were the "proper" size.
My first thoughts are
1. disconnect the caps
2. Run the motor check run amps and make sure there are no mechanical problems - run at full load and make sure the overloads do not trip.
3. Double check the control wiring to ensure the main relay opens to keep the motor from single phasing when overload(s) trips.
4. I guess because I learned it in the Navy I still like an overload for each of 3 phases.
5. If all is OK reconnect the caps and try same sequence.
Dan Bentler