I am having problem with Power Flex 70 communicating with 20-comm D ato Devicenet . The Power Flex 70 always show the "error 75" same after to erase the error in IHM, but the red light continue flashing and don't stop, same nothing indicating flaw in IHM. I need help. Thanks.
There is a fault on the 20-COMM-D Card.
Page 4-6 of PF70 Manual:
Port 1-5 Adapter 71-75
The communications card has a fault.
Check DPI device event queue and corresponding fault information for the device.
PowerFlex 70 Manual:
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/20comm-um002_-en-p.pdf
20-COMM-D Manual:
You will have to log onto the 20-COMM-D with the PF70 HIM, find out what the error is, and rectify it.
Stu....
Hello again!
I have a quick question, so I'm just going to continue in this semi-related thread.
There is a Micrologix 1500 and PowerFlex400 connected vie DeviceNet. Is it possible to program parameters of PowerFlex via DeviceNet?
Similar Topics
Hi all I am working on a retrofit project. There is one backup pump with Powerflex 753 drive controlled by 2 different PLCs(one 1756-L63 ,one...
Replies
3
Views
1,536
Hi - I have done some searching and answered a lot of my questions but..... I have a Powerflex 40 drive communicating to an 1769-L35 over...
Replies
10
Views
2,363
Power flex 527 Network based safety drive had faulty and alarm pop up SOS Code internal fault Unable to set or clear the fault manually or...
Replies
5
Views
116
Hi all. Would anyone happen to have the Modbus register datasheet for the Honeywell/EnergyICT EIMFlex Modular Meter v1.11 We've 40 of these that...
Replies
0
Views
66
I have an issue with Power Flex 525 during running processing, the VFD stopped suddenly while the PLC and VFD connection ok, VFD does not have any...
Replies
1
Views
126
Back
Top Bottom