Power Flex 755 VFD
jarvism
Jan 2017
Graham
A little background at my complex we run power flex 755 VFD's 480V most of them are 361 Amp. They are etherneted to a controller the VFD has a static IP. Also running ver. 7.002 in it. The Controller is a L61 Allen Bradley version 19 We use them to run belt drives. I ran into a problem yesterday, This drive started giving a drive fault code of 13037 which is Net I/O Timeout. I havent ran into this before and the internet isn't giving much help on this issue. was wondering if anyone else has had this issue.
Fault codes on these drives start with the DPI interface number; DPI Port 13 is the PowerFlex 755 built-in EtherNet/IP port.
The common codes associated with EtherNet/IP control connections are in the PowerFlex 755 Programming Manual, and in the RA Knowledgebase article ID # 511419 (Access Level: Everyone).
Fault code 13 037 is an ordinary timeout, so it indicates that there's a network problem between the ControlLogix and the drive. It could be a bad cable, or a problem with a switch port.
If you have managed switches, take a look at the port statistics for the switch port that connects to the drive. The PowerFlex 755 itself has statistics (you should be able to get to them through RSLogix 5000's drive profile) for the Ethernet port as well. Bad connections or noise are going to show up as checksum or MAC errors.
Hi I want to set IP 172.16.27.90 in AB Power Flex 755 drive. I do set the IP by parameters 38-41 with other settings (subnet, gateway) but...
2,468
Hello, I have a PF755 that is doing something I don't understand. I have the drive tuned and it is working well however, sometimes when I tell it...
4,125
I've heard conflicting things and want some expertise here. If a 753/755 were to lose power while motor is running, will it regen on the line...
2,256
Hi; I have arranged Allen Bradley cable and adapter for communication between Laptop and Power Flex drives which picture is attached. I did try...
2,383
Hello All, Please one the powerflex 755 Drives looses itds speed reference anytime power-cycle the drive. Parameter 545 goes to default and must...
2,723