Powerflex 755 looses speed ref after power cycle
edwardeduful
Jan 2015
ghana
60
Hello All,
Please one the powerflex 755 Drives looses itds speed reference anytime power-cycle the drive.
Parameter 545 goes to default and must set again.
Please what can be causing this, is there any other parameter i must set for this to stop.
Please your contributions will be much appreciated.
Thanks,
If it's networked to a Compact Logix or Control Logix PLC, it's possible that the PLC is set up to download a defined parameter set to the drive at startup (or whenever it detects a new drive). This is known as Auto Device Configuration, or ADC. The benefit of this technology is that you can swap a new drive in, and the PLC will program it up for you. The disadvantage is exactly what you're seeing - if you use the keypad to change a parameter, it will get overwritten the next time you cycle the power. To change a parameter, you have to either change it both on the keypad and in the PLC, or just change it in the PLC and then cycle the power to have the PLC do exactly what it's doing now, only with the correct value.
Thank you very much
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
263
Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
172
So I'm replacing a terminal block on the inverter board for a 755. I'm wondering if anyone knows what conformal coating would be best? I'm not...
137
Powerflex 755, running 2 weeks, and faulting with code 17 input phase loss.
225
Hi All, This is my first PowerFlex 755 drive setup and I am having an issue with when I start the drive it runs at my minimum speed 5Hz, but...
429