power wire size for 10hp motor
joaco1993
Sep 2014
newyork
237
Hi everyone !
A multiconductor wire 4x2,5mm2 would be ok ?
Normally a 10hp - 400V motor would pull 16-17A
A 4x2,5mm2 wire could carry around 21-22A according to many manufacturers,
Considering the wire will be on open strays, at open space and next to other small conductors, length of 30m max.
I know a wire of 4x4mm2 would be better,
But would 4x2,5 be a problem ?
The cable is copper and PVC
Thanks!
I don't know the specs off the top of my head, but usually the mfg of any motor would recommend power cable size in their manual, no? Some would even sell the correct cable to use?
Hi, good morning!
Section 430 of the NEC covers motors. There are tables for FLA, types of motors and references to other tables for the correct conductor size based on the parameters I listed above.
It may also be that you're installing AC power cables in a tray that has analog and 24 VDC. There are many considerations to take into account when one mixes cable types and voltages. Hope this helps.
Hello folks, Trying to understand wiring rules for the PLC cabinet. Per NFPA79 13.2.4.1: "The colour ORANGE shall be used to identify ungrounded...
2,214
Good day everyone. I need to install an interlink wire for run signal from 1F panel to 2F panel. Approximately the total length would be 200m...
2,603
An analog Transmitter (Sensor) with 2 wire and 4 to 20 mA output, is connected to an analog input module. The sensor requires an external 24 vdc...
2,216
Quick question: Can I run 24VDC signal wire (shielded) in the same 1 inch conduit with 2 cables (+ & -) with 90VDC to power a permanent magnet DC...
2,752
Hello, I've a question regarding wiring analog inputs (4-20mA) to a compact-logix 1769-IF8 module. The PLC and module exist already and are wired...
6,808