Hello, I recently replaced a power flex 525 drive which has identical parameters and is controlled via a logix 5573 controller.

I have run into a snag being the drive running the motor is going the wrong direction which is hooked up to a pump.

I have swapped phases around and the motor still continues to run the wrong direction.

Is there a parameter in the drive I can change or does this need to be done via the plc?

I have an engineer who is going to login and change if possible via the plc but if we can't eliminate it via the touch pad that would be a better solution.

Is it controlled over Ethernet also.

Thanks

drive in fwd.jpg
 
I am not a electrician by trade, but if your pump is going in one direction and you swap 2 of the leads and it is still going in the same direction, I would start by polling the cover of the motor and double tjek that this is facts.

I can't see how this i possible.
 
If the drive always says FWD on the front and you swap only 2 phases to the motor, then it will run in the opposite direction.

Don't take offence, but you are only swapping 2 of the phases and to the motor and not the drive?

Are you looking at the right motor?
 
Yes I am looking at the right motor, How do I get the fwd to display Rev

Swapped blue and white around at the motor terminal block
 
Tried the reverss key it is locked out due to being controlled via plc, paramter 544 doesn't change anything tried that already.
 
can you inhibit the drive and change the parameter. Is the drive in Stop mode?
There is also a chance that is disabled from the plc logic
 
Can you go in the drive properties in the plc program and change it from there. What does the parameter A 544 read .??
if it is 0 means reverse enabled
If it is 1 means reverse disabled
 
Last edited:

Similar Topics

Hi all, I have a powerflex 525 where there is no voltage coming out to the motor. The drive was reset to factory defaults with stop and saftey...
Replies
13
Views
2,785
I had to replace 3 PowerFlex 40 multi-drives that each had 3 PF4M daisy chained off the DSI port. The PF40s had comm-e cards installed for...
Replies
9
Views
2,437
Hi I have a powerflex 525 that is connected on ethernet to a compactlogix and is on ADC , I have just changed a setting on the drive and if I...
Replies
4
Views
1,825
I have a machine with a CompactLogix ver20 and PowerFlex 40 multi drive node. That PF40 has a Comm-E ethernet adapter and has four PowerFlex-4Ms...
Replies
0
Views
1,893
So we replaced a PowerFlex 525 drive with the exact same model. I was told that once it is in and given the old IP address, you can upload the old...
Replies
24
Views
14,353
Back
Top Bottom