Powerflex 525 Intermittent Decel Issue
JZerb
Oct 2016
Here
423
so i have a powerflex 525 that im controlling via the terminal blocks DigIn's. Im using DigIn 6 for my other preset frequency, which ends up being A412 and that also allows me to use accel/decel 2 with that. the motor in question runs at 30hz when the DigIn 6 input is open, and runs at 60hz when the input is closed.
P041 is 12 seconds
P042 is .2 seconds.
A442 is 8 seconds
A443 is .2 seconds.
A410 is 30hz
A412 is 60hz
Once the machine hits a certain windows within the ladder logic it then turns on the PLC output and that is what controls my DigIn 6 on the drive.
If the machine is running in the 60hz range and i let off the pushbutton on the HMI the machine stops as it should immediately. My issue is when the machine is running at 30hz, it sometimes acts just as it does in the 60hz window, but then sometimes the brake engages and the motor sounds like it trying to pull 'through' the brake.
Whats throwing me for a loop is that fact that this in only happening intermittently. and i am unable to recreate the issue with any consistency. There is a dynamic brake resistor installed on the VFD, and A437 is set to 1. I have also set A550 to 0 since i am trying to stop the motor quickly. I can watch the ladder OTE turn off on my laptop, as well as see the light on the PLC screen itself turn off thats goes to the VFD for the FWD or REV command, BUT when this issue happens i can watch on the VFD screen that the RUN command on the display is still showing up. I thought perhaps it was noise that could have possibly somehow been keeping that input on the VFD hot for longer then needed, i pulled the control wiring out of the panduit and far away from any high voltage and nothing changed. Im perplexed and open to question comments and concerns.
Is this a new problem on something that has been running fine, or is the equipment on the new side?
Bubba.
For starters you could watch the parameter that displays the terminal block status to see whether the drive is actually losing the run input.
P041 is 12 seconds
P042 is .2 seconds.
A442 is 8 seconds
A443 is .2 seconds.
A410 is 30hz
A412 is 60hz
Since you can see on the VFD that the run command is still there, I will ask what sort of output you are using. Solid State PLC outputs 'leak' a bit. And the inputs on the drive require a certain minimum on-current, but once they are on they take a smaller amount of current to 'stay on'. If the leakage is close the the minimum ON current, you will see this sort of thing. A resistor that is sized for appropriate wattage - maybe 1W - that pulls the VFD input low has typically worked for me when connecting PLC outputs to inputs on VFDs, and PLC outputs to inputs on other PLCs (back in the old days of hard-wiring systems together)
On a 24VDC system, a 1K pull-down resistor will draw 24 mA and dissipate just over 1/2 watt when the output is on. It's bit of a waste of power, but it should fix things.
Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
235
Im trying to teach a couple of labs on VFDs at a community college. We have some motor control trainers with P525s and 3 phase motors from...
247
New to vfds. I put in parameters. IP, but I get ethernet flashing and link solid. What did I do wrong?
475
Are the N files in the 525 the same as the 40p for ethernet? (E-Comm card) I have used 40P with Micrologix 1400 Messaging but don't see the N...
234
Hey all, I am currently working on a depalletizer for a customer and we are doing a hoist upgrade. This is a SLC500 processor and the drives are...
299