PowerFlex 525 Multi-Drive control on EtherNet/IP
Oct 2015
Melbourne
23
Hi All,
Tearing my hair out! I have had this working in the past but cannot figure out what is wrong now!
Simple set up.
PF 525 set up as Master in a multi drop scenario. If I don't configure any slaves, all good, can see it with Logix desginer, connects, see params etc.
PF 525 set up as slave. Simple config.
As soon as I set Master to have one connection, (param C175 = 1), and connect cable to DSI, then it's gone. Can see it, but connection produces a fault. Match drive produces a project mismatch and want to delete the slave from its params.
It is setup very simple. I've double and triple checked everything I can think of. All have been flashed to latest firmware. Reset to factory defaults multiple times.
I'm leaning towards a slave parameter mistake based on the above, but I cannot find it.
I have used the AB Applications notes: PowerFlex 525-Class Multi-Drive control on EtherNet/IP.
It is simple and should get it going, but I'm lost!
Any help appreciated.
(Router connecting PLC and VSD is a TPLink, but should be fine as it is holding the entire PLC network together with no issue.)
GT.
I had to replace 3 PowerFlex 40 multi-drives that each had 3 PF4M daisy chained off the DSI port. The PF40s had comm-e cards installed for...
2,435
I have a machine with a CompactLogix ver20 and PowerFlex 40 multi drive node. That PF40 has a Comm-E ethernet adapter and has four PowerFlex-4Ms...
1,893
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
33
Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
239
Im trying to teach a couple of labs on VFDs at a community college. We have some motor control trainers with P525s and 3 phase motors from...
249