PowerFlex 525 Start/Stop question.

tjoneill

Member
Join Date
Jul 2007
Location
Michigan
Posts
66
Hi all.

Having a problem with a PF 525 TermBlk 5 input.
I came across the drive the other day and not sure how its running.
Both the Enable, and run/fwd is hot all the time (Term 1,2), but when Input Terminal 5 is hot, the motor stops, when its not, the motor starts. That is how they are starting/stopping the motor.
Setpoints are:
P046,48 Start Source 1,2 are both DigIn TrmBlk
P047.49 Speed Reference 1,2 Drive Pot
T065 DigIn TermBlk 05 is set too 7 preset Freq.
I am going to have to change the PLC Program to start and stop from terminal 2 and jog manual from Terminal 5 but not sure how it is even running the way it is. Any input is appreciated. Thanks again.

Sorry...PowerFlex 523
 
Last edited:
It sounds like it is set to run all the time, and terminal 5 sets preset speed to zero, so stops the motor.
I cannot imagine why anyone would do that.

I suggest read the manual and check every parameter, and configure with improved start and jog controls as you say.
 
That is exactly what was going on. Finally found 1 sentence in the manual that said Terminal 5 (t065)is set to 7, then the default for F010 is 0 hz.
So someone was using a Output from the plc (controlled by a sensor) to Terminal 5, set to Preset Zero, with a speed of 0 hz.
Damn.
 
That is exactly what was going on. Finally found 1 sentence in the manual that said Terminal 5 (t065)is set to 7, then the default for F010 is 0 hz.
So someone was using a Output from the plc (controlled by a sensor) to Terminal 5, set to Preset Zero, with a speed of 0 hz.
Damn.

Maybe a fail safe attempt? If the PLC ever failed, the VFD would continue to run at whatever the last commanded speed was which, depending on the application, might be the desired result.
 

Similar Topics

Hi All, I have been asked to commission two new Powerflex 525 vfds on site which I've never done before and I've ran into a problem which I'm...
Replies
3
Views
1,407
Good Morning , I would like to start a Powerflex 525 with a N.O. Start Pushbutton , and when the N.O. Start Pushbutton is released I would...
Replies
3
Views
1,674
Greetings Fellow Controls Professionals, I have a weird issue with starting a 2HP PowerFlex 525 VFD. The drive is commanded through Ethernet IP...
Replies
2
Views
1,485
Hello everyone, I am new to this site and relatively new to PLC have had a few college courses. I am now working on my Masters Capstone Project...
Replies
2
Views
1,942
Good Afternoon , I have several new PowerFlex 525 drives. 5 drives out of 17 will start thru my Compactlogix start signal . The rest will...
Replies
19
Views
16,192
Back
Top Bottom