Powerflex 70 decel rate in 2 wire control
spice_miner
Aug 2006
Iowa
45
I have a machine with a Powerflex 70 drive. It came from the OEM wired 2-wire control. Changing decel 1 time has absolutely no effect on the drive. I talked to one of Rockwell's engineers and he told me that the Powerflex 70 when in a 2-wire configuration, only uses "coast" as a stopping method. The decel 1 parameter does not apply. Can anybody confirm or deny this statement? I find nothing in the manual to back this up. I wired the drive up in three wire control and after changing decel 1 to 5.0 from 3.5 I saw a change in the way the machine stopped. I ended up at 10.0 on the decel rate and was almost where I wanted to be but it caused other problems with the machine. It has a cycle stop and it didn't like 10 seconds as a ramp rate. I watched the frequency on the drive in 2 wire and in 3 wire. The 2 wire set up didn't have a ramp at all.
I am not 100% on the Powerflex 70, but for the other Powerflex families (4/40) the Terminal 01 input is always coast to stop unless you are in three wire control.
When using two-wire control, and you want a ramp stop, just remove the Run/Forward or Run/Reverse command, leave the stop input high (not stopped) to let the drive ramp down.
In two-wire control, the "Stop" terminal is basically an Enable.
so i have a powerflex 525 that im controlling via the terminal blocks DigIn's. Im using DigIn 6 for my other preset frequency, which ends up being...
2,090
We use Powerflex 70 for a 3phase 480V motor that pulls a coil off a coil reel. A vertical laser (Allen Bradley 45cpd analog laser sensor)...
30,602
I've got a Powerflex 700 that doesn't like to get going in the mornings. This motor will run anywhere from 30 seconds to 5 minutes before it just...
164
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
265
Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
172