Powerflex 70, DNet, Control Logix
Adam Bullen
May 2012
Taupo
Hi;
I am converting a PLC5 to Control Logix; I have a bunch of DNET Powerflex 70 drives.
I have used the tool to build my data base; and I'm wondering what the OutputCurrent_0....15 bits are?
Is this a binary representation of the motor current or %FLC? I have found all of the information I need in the manual except any mention of these bits.
Do you know if they are the older "Standard Control" drives, or the PowerFlex 70 "Enhanced Control" ?
If you've got your DataLinks set up for Parameter 3, that's probably where the drive is getting the enumerated Output_Current parameter.
Since it's evidently 16-bit, it's probably a Standard Control drive.
Parameter 3 Output Current is the output current of the drive, in units of 0.1 Amperes for Standard Control drives, and units of 0.01 Amperes for Enhanced Control drives.
So a value of "100" would probably indicate 10.0 Amperes.
Thanks for the reply.
It is the enhanced control option; "20AD034... (Enhanced option)" from RSNetworx.
So this will have to be mapped into an INT to give amps x 100? Seems weird that it doesn't come across as a INT like the feedback parameter.
Hi! I have a PF700H, 600V, 590A. Its on DeviceNet. Produce Type: 121 Product code: 45620 Revision: 1.006 EDS File I think I need...
1,446
Hi all.....thank you for looking I'm working on a project with 2 Powerflex 700 VFD drives with 20-COMM-D DNet adapters. The 20-COMM-D has the...
2,632
I've got a Powerflex 700 that doesn't like to get going in the mornings. This motor will run anywhere from 30 seconds to 5 minutes before it just...
164
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
265
Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
172
