fiveliter8
Member
Good day everyone! We have several laminar flow hood blowers controlled using powerflex 70 drives that are tied into our building management system (siemens). Our BMS is programmed to attempt re-start of the drives if it sees both a fault and not running output from the drives. When we get a power outage, all drives restart as they should by our BMS once power is restored. We also receive periodic power sags that last shorter than one second, and when this ocurrs, the drives drop output to the blowers, latch a not running output (which BMS recognizes) but never faults. We can re-create the situation manually with the mains disconnect. What we found is as long as the display on the drive remains on from residual power after mains is lost, and then mains is restored, the drives behave the same way as during power sags. On our equipment that use powerflex 700 drives, we don't have this issue. Looking at the manual for the drive, it would seem the undervoltage limit is hard-set and not adjustable, as we don't see a parameter to adjust this. Is there something we are missing? Our controls engineer is dead set against modifying the BMS program to attempt restart without the fault signal from the drive (and all the red tape that goes along with it). Is this an inherent issue with the 70 and we are stuck with manual restarts after sags?