I'm attempting to add a PowerFlex 755 using the "Discover" method in a ControlLogix program. I match it to the drive, add a few datalinks that I want, and then click "Create" and after a minute it says that it failed because the slot is in use by another module. What in the world does that mean? I've added plenty of modules using this method, and this is Ethernet, not a slot.
First your buss voltage is way too low
For a 400V input it should be about 687 VDC and for 480v input it should be 825 VDC with no load
What you describe tells me that you have a single phase condition possibly a blown power diode to DC buss
” This drive is connected to a motor with a nameplate that gives both 400V / 50 cycle and 460V/60 cycle nameplate values. (An SEW gearmotor).”
That tells me that it is a 4 pole motor, base speed at 50Hz would be 1500RPM and at 60Hz it would be 1800RPM
From your description they want to run it in over speed 70 – 90Hz range, that is doable and is done all the time. As we all know no standard motor will run at it’s base speed they all have to slip to develop torque so the normal rated speed for a 4 pole 60hz motor is about 1750RPM. I have run 4 pole (Base Speed 1800RPM at 120Hz many times without any problems
As for de-rating the drive should not be necessary
Keep in mind that with a standard motor if it’s running below base speed it is running in constant torque variable HP mode and above base speed it is running in constant HP and variable torque mode so the drive should not need to be rerated. Below base speed / frequency the vfd will supply a constant volts to hertz ratio. 8volts / hertz, above base speed the supplied output volts to hertz ratio is reduced The voltage to the motor remains constant while the output frequency goes up.
A motor running at synchronous speed develops 0 torque, that’s why the label always show a speed less then synchronous speed it call slip. Example a nameplate rating of 1750 RPM is a 4 pole motor base speed of 1800 RPM the motor is fully loaded when the RPM’S slip down to 1750
As you can see don’t really don’t need to reduce the supply voltage to 400
The motor has is rated 400V 50hz / 480V 60Hz in the US the normal line voltage is 480V 60HZ
With running the motor at the higher frequency / speed you would be better to use the standard 480V supply this would give you more voltage available for the higher frequency you want to run at.
I would recommend that you replace the vfd with a Yaskawa brand I am sure it will give you much better performance then what you are using.
Let us know what you find
Gary, I think you meant to reply to another thread. :)
After some more digging and chatting with Rockwell, I found another Tech Note that led me to finally resolving this, so I will post this here for anyone else (or future me when I forget what I did) that runs into this.
I had to upgrade the AOP for the drives.
Then, instead of choosing "Discover Modules" I had to choose "New Module" and then match the drive that way. The tech did some digging and found this to be a known issue and they have notes about it internally, so hopefully this gets resolved.
Hopefully it also makes it to the Knowledgebase and release notes as a known anomaly so we can access the information without needing to go through what you just did...
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
306
Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
190
So I'm replacing a terminal block on the inverter board for a 755. I'm wondering if anyone knows what conformal coating would be best? I'm not...
148
Powerflex 755, running 2 weeks, and faulting with code 17 input phase loss.
234
Hi All, This is my first PowerFlex 755 drive setup and I am having an issue with when I start the drive it runs at my minimum speed 5Hz, but...
446