PowerFlex700VC Output Current

dondon_alba

Member
Join Date
Aug 2009
Location
Bahrain
Posts
35
Is this a normal phenomenon that the time I give a stop command to my VFD I can see that the “Output Frequency” is Zero, but I still get an ‘Output Current” and at the same time the VFD is also showing “At Speed” displays on the HIM. It will take for about 3 to 4secs before ‘Output Current” goes to “Zero” and the “At Speed” change to “Stopped”. VFD deceleration time is set 5secs.
I am having a PowerFlex700VC drive, 400V, 56A with a 20-CommD adapter. What I understand (maybe I’m wrong) is that when you give a stop command to the VFD after the deceleration time set elapse the VFD will shut down it circuits immediately and goes OFF.
Thanks, hope someone could enlighten me.o_O
 
Sounds like the drive is set up to either do a DC injection braking stop or maybe a DC hold after stopping. In either case, the frequency will be zero but the amps will be up at some significant value.
 
Since my VFD is connected through a device net network I found today that the stop command has been delayed by 4secs in other words even if I see that the output frequency is zero, there is no stop command given to the VFD because of the time being set.

It’s my bad, just found it today.

Thanks DickDV. We don’t used the DC injection braking and the DC hold.
 

Similar Topics

Good Day Everyone, I’ve been reading this forum whenever I get time and very pleased with the various information given that in the end help me...
Replies
8
Views
6,314
Hi There, I have a filler with a coriolis flowmeter that has died. the filler requires a pulsed output (manufacturer wont edit the program) is...
Replies
13
Views
260
Hey all, I am starting a new project for a customer and I am adding in solenoid valves. Once added, I noticed there was a lack of an Output...
Replies
0
Views
89
Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
Replies
4
Views
191
Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
Replies
1
Views
127
Back
Top Bottom