I have a pressure transducer:
sensotec
A = + supply
B = - supply
C = - output
D = + output
EXE/SUPPLY 9 - 28 VDC
OUTPUT 0 - 5 VDC
The analog in card is a F2-08AD-2
Wiring to the card is as follows
A = 24VDC
B = 0VDC
C = 0VDC
D = Channel
trying to read
jumpers on +1,+2,+3 are all off
jumper on j3 is on for 5 Volts
My program is as follows
PLC 250(-1)
// Rung 1
// Address 0
STR SP1
LD K100
OUT V7660
LDA O2000
OUT V7670
LD V2000
MUL K500
DIV K4095
OUT V2500
// Rung 2
// Address 9
END
// Rung 3
// Address 10
NOP
in data view i'm viewing the v2000 and v2500 but both values are the same is that how it is supposed to be? I was expecting to read the psi value since i multiply by 500 and divide by 4095?