Pressure Transducer on DL205-1 F2-08AD-1
Tommycai
Aug 2011
KY
120
Pressure Transducer is a FPG2CR,2D5D6A SENSOTEC,
Range: 500PSIG
Supply: 9 - 28 VDC
Output: 0 - 5 VDC
A (+) Supply
B (-) Supply return
C (-) Output 0 Vdc to
5 Vdc
D (+) Output
E No connection
F No connection
I HAve wired up pins as according:
A = RED
B = BLK
C = GRN
D = WHT
my question is that, am I to wire together pins B and D together?
I connected pins
A to +12.24V on PLC Power supply
B to 0 VDC on Analog Card
C CH 1.
D is that to be connected to 0 VDC as well?
Treat the supply as floating. A&B are power supply only.
C&D go to Analog card only. If polarity is wrong, swap C&D.
IF that doesn't work, then treat the supply an non-floating. Wire A&B to the same power terminals as the analog card. All 4 leads will be going to the analog card.
I'm just confused about the card since it only has channel inputs ie
0V
24V
ch 1+
ch 2+
ch 3+
ch 4+
ch 5+
ch 6+
ch 7+
ch 8+
Pins A B are on 24 and 0 V
Pins C D are on ch1 and 0 V
got this working now trying to convert value from pressure transducer into psig thank you .
I have a pressure transducer: sensotec A = + supply B = - supply C = - output D = + output EXE/SUPPLY 9 - 28 VDC OUTPUT 0 - 5 VDC The analog...
2,418
Good morning everybody, I hope you are very well. I share with you the information of the PLC LOGO! Siemens and expansions that we have...
1,098
Has any used a ballistic pressure transducer with a PLC? I am not sure if it will capture the event that I need to use as a control. The device...
1,087
I am updating controls on a leak tester, from a SLC 5/02 to Compact Logix. The SLC used a DDV instruction to help scale a differential pressure...
17
4,431
A little background info I work at a underground coal mine. We have a Dust tank capable of holding 135 tons of rock dust on the surface. We use...
1,680