Pressure transducer program?
sas11
Mar 2008
Virginia
36
Would it be possible for someone to supply me with a couple rungs of programing or a simple program.(Direct logic from automation direct)showing some logic for pressure transducers. Currently using a pressure switch and would like to incorporate a transducer in its place.
o_O
OK, shall we try this again?
There isn't enough information in your post to answer your question.
First, I suggest you do a forum search for posts by our distinguished colleague Ron Beaufort using the keyword scale. He has written several very informative tutorials here about scaling analog values. They are also on his website.
Then fill in the following pieces of information:
  • What are the pressure units of your transducer? PSI? Bar? Pa? inHg?
  • What is the pressure transducer minimum pressure?
  • What is the transducer's output at that pressure? mA? Volts?
  • What is the pressure transducer maximun pressure?
  • What is the transducer output at that pressure?
  • From your PLC analog input card specifications, what is the raw value from the A/D converter when the input is equal to the minimum pressure, milliamps or volts?
  • From your PLC analog input card specifications, what is the raw value from the A/D converter when the input is equal to the maximum pressure, milliamps or volts?
Once you gather that information and write it down I think you will see exactly what you need to do.
Good morning everybody, I hope you are very well. I share with you the information of the PLC LOGO! Siemens and expansions that we have...
1,097
Has any used a ballistic pressure transducer with a PLC? I am not sure if it will capture the event that I need to use as a control. The device...
1,085
I am updating controls on a leak tester, from a SLC 5/02 to Compact Logix. The SLC used a DDV instruction to help scale a differential pressure...
17
4,429
A little background info I work at a underground coal mine. We have a Dust tank capable of holding 135 tons of rock dust on the surface. We use...
1,666
Hi Guys, Is a typical transducer programmed to output its signal in intervals? Say every 10 seconds it would generate a signal via 4-20mA loop...
1,657