Problem with downloading TwinCAT 3 project
Dusan_QC
Jan 2020
Belgrade
Hello everybody,
I have a problem with TwinCAT 3. When I try to activate a configuration and start IPC in Run mode I receive an error AdsWarning: 1810 (0x712, ADS ERROR: server is invalid state) and it stays in Config mode.
I have IPC from the IPC series CX51x0, devices on its own reck and EtherCAT couplers (see attached picture) and when I try to activate a configuration and start IPC in Run mode with only a few variables linked in the hardware configuration, it works, but when I link all variables in the hardware configuration, it raises above-mentioned error.
Do you have any suggestions on what to do or try?
Thank you in advance.
Check your hardware config, device 2 is not swapping from SAFEOP to OP Mode. on TWCAT2 this used to be becasue the IO didn't match, haven't used TWCAT3 much
As far as I see it you should only have 1 EtherCAT master, (your CX51x0) and your EL6631 should be a box on your EK1200. Your EK1100 and BK1120's should be appended terminals on you EtherCAT master. Verify your topology against your physical setup.
Hello everybody,
As others also said,this error code stem from the discrepancy between your configuration and your physical modules. You have to check your configuration exactly.
Dear Friends Please I face problem with Simatic PLC S7-415H , I can go online throw IP/TCP network and uploading the logic from PLC too PC but...
1,791
Hi guys!! Back again with another issue... Im currently working with Crimson 3 and a G315 HMI. While working on a database I previously...
2,462
Hi All! I added a combination I/O module 1794 IE4 XOE2/B to the end of 1794 RIO devicenet node. In RSNetworx for Devicenet V11 (CPR9) for some...
5,167
I have a Q00 PLC from a customer who want to modify some in Main program. First I upload program from PLC using GXWork 2. Everything is ok. But...
4,439
I am trying to download Rockwell's RSLogix emulator from their free downloads. However, after I click it and sign in all it does is go through a...
2,143