I write also to communicate some problems with the 1756HP-TIME module of HIPROM.
In particular:
• The manual "Integrater Architecture and CIP Sync Configuration" Rockwell Automation (p. 98), states that the minimum revision of the firmware for the HP-TIME module is 3.0, but that version of the firmware is available to download from the web page official "http://www.hiprom.com/Pages/Products/1756_CLX/1756HP-TIME/web/1756HP-TIME.htm";
• There are problems on all machines on which it was tested, opening the configuration module HP-TIME in RSLogix 5000, in particular the software crashes open the tab "TimeSync" as shown in 'image attached.
Thanking for the availability
Sincerely
can you post a link to RA publication that states 3.0 FW?
the latest firmware of 1756-TIME is 2.02.04 and it works with Add-On profile 2.01.10
Once you have these, to see CIP sync data you must enable CIP SYNC under "configuration" tab first
Also remember that module does not do CIP SYNC via backplane like EN2T does. You technically must have ethernet connection between EN2T and TIME to get time to the processor
Hi thank you very much for your answer!
As you've explained above, I've been able to sync the CPU only using the EN2T module.
About the firmware, you can find the pubblication in the following link http://literature.rockwellautomation.com/idc/groups/literature/documents/at/ia-at003_-en-p.pdf
Se for example page 12, 94, 98 ect...
Thank you again
Sincerely
I am pretty sure that FW 3 is mistake
I will check with my sources and get back to you on that
My module FW 2 is in simulation mode and with CIP SYNC enabled it becomes the system grandmaster over Ethernet without any changes in default parameters.
Make sure you leave Priority 1 as default on all modules
From that moment all EN2T should take it as a master and propagate time to the processor.
If this does not work, then I recommend you to contact your regional RA support center so they can ferify profile rev, and configuration settings.
Without details I can't say what you are doing wrong.
Can you post screenshots of all tabs?
Please ZIP them first so we can see details
Now all works!!! The Rockwell software no longer crashes!!!
Thank you very much for your attention!!!
Hello, I am a plc engineer and I have a job to do in the NIGERIA 25000 TON GRAIN SILOS STORAGE CONTROL PANEL. A problem where the panel is not...
151
The project on the operator workstation keeps disconnecting, even though I have an installation server and operating station set up through...
64
I have a problem, I'm running an AE Licence Manager on a Windows 2016 Server, and my Window Maker is on another separate Windows 2016 Server. My...
96
I have one old Ansaldo VFD from 37kW and it have only sign OFF on the display after put it on the 3x400VAC. Is there any idea, how to solve this...
88
23
655