Problem with HIPROM HP-TIME and RSLogix 5000

peterpan405

Member
Join Date
Feb 2013
Location
Milan
Posts
7
I write also to communicate some problems with the 1756HP-TIME module of HIPROM.
In particular:
• The manual "Integrater Architecture and CIP Sync Configuration" Rockwell Automation (p. 98), states that the minimum revision of the firmware for the HP-TIME module is 3.0, but that version of the firmware is available to download from the web page official "http://www.hiprom.com/Pages/Products/1756_CLX/1756HP-TIME/web/1756HP-TIME.htm";
• There are problems on all machines on which it was tested, opening the configuration module HP-TIME in RSLogix 5000, in particular the software crashes open the tab "TimeSync" as shown in 'image attached.

Thanking for the availability

Sincerely

cccc.jpg
 
can you post a link to RA publication that states 3.0 FW?

the latest firmware of 1756-TIME is 2.02.04 and it works with Add-On profile 2.01.10

Once you have these, to see CIP sync data you must enable CIP SYNC under "configuration" tab first

Also remember that module does not do CIP SYNC via backplane like EN2T does. You technically must have ethernet connection between EN2T and TIME to get time to the processor
 
can you post a link to RA publication that states 3.0 FW?

the latest firmware of 1756-TIME is 2.02.04 and it works with Add-On profile 2.01.10

Once you have these, to see CIP sync data you must enable CIP SYNC under "configuration" tab first

Also remember that module does not do CIP SYNC via backplane like EN2T does. You technically must have ethernet connection between EN2T and TIME to get time to the processor

Hi thank you very much for your answer!

As you've explained above, I've been able to sync the CPU only using the EN2T module.
About the firmware, you can find the pubblication in the following link http://literature.rockwellautomation.com/idc/groups/literature/documents/at/ia-at003_-en-p.pdf

Se for example page 12, 94, 98 ect...

Thank you again

Sincerely
 
I am pretty sure that FW 3 is mistake
I will check with my sources and get back to you on that

My module FW 2 is in simulation mode and with CIP SYNC enabled it becomes the system grandmaster over Ethernet without any changes in default parameters.
Make sure you leave Priority 1 as default on all modules

From that moment all EN2T should take it as a master and propagate time to the processor.

If this does not work, then I recommend you to contact your regional RA support center so they can ferify profile rev, and configuration settings.

Without details I can't say what you are doing wrong.
Can you post screenshots of all tabs?
Please ZIP them first so we can see details
 
Last edited:
I am pretty sure that FW 3 is mistake
I will check with my sources and get back to you on that

My module FW 2 is in simulation mode and with CIP SYNC enabled it becomes the system grandmaster over Ethernet without any changes in default parameters.
Make sure you leave Priority 1 as default on all modules

From that moment all EN2T should take it as a master and propagate time to the processor.

If this does not work, then I recommend you to contact your regional RA support center so they can ferify profile rev, and configuration settings.

Without details I can't say what you are doing wrong.
Can you post screenshots of all tabs?
Please ZIP them first so we can see details

Now all works!!! The Rockwell software no longer crashes!!!

Thank you very much for your attention!!!
 

Similar Topics

Hello, I need to write the following program in Ladder language, but I could not integrate the Fibonacci sequence into the ladder. Can you help...
Replies
11
Views
150
On all pages of my project i have a lot of information, texts and details that should not not be shown. I can remove them for each part apart from...
Replies
0
Views
41
Hi, I have had problem with upgrading some projects from v16 to v18. I tried it on 3 diffrent computers. I want to post this so that anyone that...
Replies
3
Views
182
Hi, I am having a challenge installing a new drive ACS355-03E-44A0-4 as it keeps on displaying Fault code F00018 even when the load is not...
Replies
3
Views
135
I have an issue on my vessel, we have water tight door system created in China, company is no longer operating. We have 7 doors each with their...
Replies
4
Views
147
Back
Top Bottom