I am not sure if the 1100 has that data type, the version of RSLogix500 I have at work is too old. I know the 1500 supports the Ls. Do you get the option for Long when you create a new data file? According to this PDF: http://literature.rockwellautomation.com/idc/groups/literature/documents/sg/1763-sg001_-en-p.pdf the 1100 should support longs (double integer data file support, page 6 of PDF).
If you can get the data into L registers, then yes, the data will transfer as the same value. However it appears that the PV and the SP have 3 implied decimal places. If this is the case a PV of 100 (100.000) will transfer to the PLC as 100000. Likewise of you need a setpoint of 100 (100.000) you will need to send 100000 from the PLC. If this is the case and it is not programable, you can just multiply (or divide depending on direction) your exisiting N registers by 1000 and place the result in a L register.
Regards,
If you can get the data into L registers, then yes, the data will transfer as the same value. However it appears that the PV and the SP have 3 implied decimal places. If this is the case a PV of 100 (100.000) will transfer to the PLC as 100000. Likewise of you need a setpoint of 100 (100.000) you will need to send 100000 from the PLC. If this is the case and it is not programable, you can just multiply (or divide depending on direction) your exisiting N registers by 1000 and place the result in a L register.