Problem with Panelview plus 700
Revnus
Aug 2019
Brazil
73
Hi. I'm working on a plant that has a panelview plus 700.
Problem is that from time to time, the alarm list shows an old false alarm instead of the real alarm. For example: Instead of "emergency active" it will show "low pressure", which is an old alarm that is already ok.
Operators at the area try to find the alarm for a long time, until they realize it is a false alarm. Then they shutdown the runtime application using a screen button leading to the panelview builtin options, and then they run application again. Doing this process, the real alarm will show, not the false one.
Since I dont have any better clue, I tried to create other .MER using remote clear history function from FTViewME, but the panelview firmware does not support runtime version that have this function..
Other option would be to reset the runtime using logic, shutting down automatically instead of operators doing it manually when they notice the alarm is not real, but I dont know how to do it.
I suspect the problem might be something related to logs or cache, but what can I do?
The time that the area operators spend trying to find what is causing a fake alarm is really expensive to the plant. If I cant find a solution, I think they will have to buy other HMI.
Other info:
- Latest firmware listed in SCDC for panelview plus 700 is 5.1, but when I go to terminal settings, it shows ME Station 6.0.
- Intermitent problem. It might not happen for a week or a month.
- I will try to increase the number of alarms (128 now), this will delay the problem but wont solve. What is the max number of alarms in PanelviewPlus 700, btw?
Discovering the solution for the real problem (Cache? Logs?) will be great, but a other solutions as showing how to to shutdown the Runtime automatically, are ok aswell.
Thanks!!!
Hi. I'm working on a plant that has a panelview plus 700. Problem is that from time to time, the alarm list shows an old false alarm instead of...
2,763
Hello,im a student and i have to do a project using a Panelview plus 1000.I have configured my device shortcuts with the right PLCs in design and...
3,511
Hi guys, i am working on a project using PV+, there is a problem for the alarm history display: 1. first, to clear the alarm history. 2. create a...
2,573
Above mentioned HMI is installed in my plant with Micrologix PLC. Yesterday the HMI suddenly stopped working during plant operation and HMI's...
4,938
I just recently replaced a panelview 600 with a panelview plus 700 and I am new to programming plc's so bear with me . I got the panel builder 32...
1,410