Hello guys,
Today I have experienced very strange problem with SM431 module 16 inputs x13 bit. On this card, there are 12 4-20 mA signals coming from Pt100/4-20mA transmitters
After 10 years of working majority of measurements went out of range. We have measured mA from the field and concluded that module has failed. We have replaced the module and everything worked for 3-4 hours and and happened similar but this time all measurements are in measuring range but showing significantly less than expected.
So we measured again and noticed some strange. We disconnected the filed and connect to the terminal strips in the cabinet 4-20mA Fluke simulator. We have checked all wired inputs. The results are the following:
Ch1 : 4mA -> 32767, 12mA -> 2600, 20 mA ->14400;
Ch2: 4mA ->32767, 12 mA->2800, 20 mA ->15000;
Ch3: 4mA ->32767, 12 mA->3000, 20 mA ->15600;
...
Ch10: 4mA ->32767, 12 mA->3200, 20 mA ->15800;
...
Therefore, one would expect that 20 mA = 27648, and 12 mA would be around 13000.
It seems that another module failed. We have checked the cables for 3 or 4 input signals from the field (from the sensors), but they seem OK, no short circuits to the ground or anything like that .
What could be the possible cause that card failed in such manner that all inputs have range disturbance, but in very similar manner?
First analog module has all inputs to 32767 and it was fairly easy to notice that module failed. But the second module is real mystery.
It is highly unlikely that two modules fail without some disturbance coming from the field. But to fail in such way to disturb the range but to show some nonlinear change is very strange.
Has anyone else had similar experience?
Regards,
Pandiani
Today I have experienced very strange problem with SM431 module 16 inputs x13 bit. On this card, there are 12 4-20 mA signals coming from Pt100/4-20mA transmitters
After 10 years of working majority of measurements went out of range. We have measured mA from the field and concluded that module has failed. We have replaced the module and everything worked for 3-4 hours and and happened similar but this time all measurements are in measuring range but showing significantly less than expected.
So we measured again and noticed some strange. We disconnected the filed and connect to the terminal strips in the cabinet 4-20mA Fluke simulator. We have checked all wired inputs. The results are the following:
Ch1 : 4mA -> 32767, 12mA -> 2600, 20 mA ->14400;
Ch2: 4mA ->32767, 12 mA->2800, 20 mA ->15000;
Ch3: 4mA ->32767, 12 mA->3000, 20 mA ->15600;
...
Ch10: 4mA ->32767, 12 mA->3200, 20 mA ->15800;
...
Therefore, one would expect that 20 mA = 27648, and 12 mA would be around 13000.
It seems that another module failed. We have checked the cables for 3 or 4 input signals from the field (from the sensors), but they seem OK, no short circuits to the ground or anything like that .
What could be the possible cause that card failed in such manner that all inputs have range disturbance, but in very similar manner?
First analog module has all inputs to 32767 and it was fairly easy to notice that module failed. But the second module is real mystery.
It is highly unlikely that two modules fail without some disturbance coming from the field. But to fail in such way to disturb the range but to show some nonlinear change is very strange.
Has anyone else had similar experience?
Regards,
Pandiani