problem with upload/download

jiten84

Member
Join Date
Mar 2010
Location
melbourne
Posts
10
hi guys,

i am vey new to plc programming and i tried to download plc program from rslogix to ab control logix 5561 through ethernet cable. but when i go to communication> who active no plc appear there...

i have installed Rslinx after RSlogix5k may be the problem?
 
Sounds to me like you don't have the communication drivers setup in Linx. This has to be done (and done correctly) before you will see the processor.
 
thanks,
i think i din't setup drives in linx. can you tell me how to setup drivers in linx if i am connecting through ethernet cable.

thanks in advance
 
Firstly - your PC and the Ethernet comms module must be in the same subnet.

You will need basic IP addressing knowledge to know this.

Secondly - Set your RSLinx driver up to browse the local subnet, and it should appear in RSWho.

Thirdly - If it shows as a "module", then you don't have the correct EDS file installed for the module
 
the boottp utility that comes with the RS linx can help find the subnet and IP if you do not know it on the processor there is a MAC address use the utility enter the MAC and it should tell you what the IP and subnet is. Keep in mind this will only work if the processor ethernet card is set to allow the boottp. The other way to find it is to connect via the 1757-cp3 cable. Daba mentions a critical step. You must configure your laptop network adaptor to the same subnet and a similar IP address
for example controller IP 192.168.11.100
set the laptop IP to the same but one off 192.168.11.101 for example usually as long as the first set of three are the same then the last 3 addresses doesn't matter as much.
 
What ethernet comms module are you using ? ENET, ENBT, or EN2T
 
there is the actual situation

i have copy of original programe. i made some changes to it according to requirements.

now ENET ip is 192.168.250.100 and subnet is 255.255.255.0
i configure my laptop 192.168.250.104 and same mask

there is project path is AB_ETHIP-1\192.168.250.100\Backplane\0
when i configure linx is comes AB_ETHIP-1\192.168.250.104

so, i am confused what is wrong with this procedure?
 
Last edited:

Similar Topics

Hi guys! I'm trying to download a project to the controller, who already has an aplication running protected by a blank password. The option to...
Replies
3
Views
2,911
Dear Friends; We have OMRON CJ1M CPU23 with I/O cards at one of our machine. We have arranged a spare PLC and tried to download the program...
Replies
6
Views
6,918
Hi Guys, Good day! I have a question here for TI505 TCP. I plan to upload and download an existing program using the ethernet port of the...
Replies
3
Views
3,024
I have not been able to upload or download programs from the ultravar 5000 series drives. I can look at the drive on line and look at...
Replies
1
Views
6,160
I have an issue. I am trying to resolve what logic is in a 90-30 PLC (364 CPU). I have 3 Machine Edition backups with different names. All show...
Replies
2
Views
156
Back
Top Bottom