Produced/Consumed Tag L23E->L55

Mike_RH

Lifetime Supporting Member
Join Date
Sep 2006
Location
Toronto
Posts
896
I have a ComapctLogix L23E, FW Rev 19.
It is has a produced tag.

I want to consume the data in a L55 FW Rev 16.
In the L55 chassis I am using a ENBT.

When I try to add the L23E to the path in the HW tree.
I cannot - the only CompactLogix listed is L32E & L35E.

So, my question - can I consume the L23E tag in the L55?
Or do I have to replace the L55?

Thanks
 
Yes, definitely you could consume the L23E produced tag within the 1756 ControlLogix Rev.16
Just add the L23E as an L32E and you will probably be just fine.
 