CLX- Ethernet Produced / Consumed tag problems
Mike6158
Nov 2003
Texas
44
For some reason I am having trouble setting up a pair of L61 controllers with ethernet cards for producing and consuming tags. I've added ENBT's and set them up per info I found on the Rockwell Knowledgebase system and the ENBT is "faulted". Not the ENBT that I use for the HMI. The ENBT that I have added for the produced / consumed tags. I only need to move 1 real and 1 word. I've set up a UDT in both PLC's. The error that I get is:
Code 16#0109 Connection Request Error. Invalid Connection Size.
What am I missing?
Mike
In your I/O configuration take a look at the second/remote ENBT module. Go into the configuration and on the General tab verify that the chassis size setting is correct. I have seen that error when I forgot to set the proper chassis size.
OG
:-( well shoot... that's got to be what it is. One rack is a 10 slot rack and one is a 7 slot rack. I overlooked that and both of the racks that I inserted are 17 slot racks. I can't change it without a shutdown and we've had a rough couple of weeks. They'll want to string me up if I have to shut them down. Thankfully the plant is running like **** and it is likely to be down within a few minutes.
Thanks for you help. Sometimes the obvious is transparent :eek:)
When you create a remote 1756-ENBT in the I/O tree, you can set it up with a "Rack Optimized" connection or a "None" connection. That mismatched I/O size error is very likely on the Rack connection.
Since you're adding a CPU in the remote chassis as a target for the Produced/Consumed Tags, you don't need the Rack Optimized connection. I think you can inhibit it and keep the Produced/Consumed Tag connection.
Either way, the mismatched size Rack Optimized connection is just a nuisance. You can safely ignore it.
Thanks Ken. The problem is that along with the error I am not getting any data transfer. Hopefully I'll get an opportunity to correct the problem and download tomorrow.
Hi All, I have two compactloxic controllers communicating with each other over ethernet. both are producing and consuming tags from one to the...
9,137
I have several Avery scale units and they are configured as Generic Ethernet modules, and I am actually reading the data fine for the weight...
422
I am trying to setup communication between two Siemens PNPN couplers and a CLX on Ethernet/IP. I have deployed a Prosoft PLX82 gateway to handle...
2,325
I setup a Flexi Soft system through the designer. All modules have green lights, except for the FX0-GENT status light flashing Red/Green...
3,448
Hi, I am currently working on a project and I have to exchange datas between a Beckhoff TwinCat 3 CPU C6925-0010 and a AB Control Logix. I was...
1,872