Profibus DP communication between two PLCs (315-2 DP)

I’ve just come back from lab.
icon7.gif
Thanks to yours tips I manage to use SFC 15/14 to send/ receive data. The main errors where the wrong LADDR parameter and error in HWConfig and RECORD parameter – there should be the same number of bytes.

Now I’ll study I_PUT/I_GET (probably till the end of the week I’ll have new questions
icon10.gif
).

Thanks again.
icon7.gif

PS Does anybody know how many bytes can be sand this metod with SFC 14/15? 32 bytes?
 
For S7-300: as many as you can configure for one slot in DP slave (depends of its type) and not more than 244 bytes (Profibus limitation).
For S7-400: up to 32 bytes.
If you reqiure more data you have to configure more I/O areas for Slave for ex. 2x32bytes but there is still limit of 244 bytes In and 244 bytes Out total.
 