Profibus drive
krome
Jan 2009
michigan
31
Hello
i have successfully got a profibus communication to the drives I am able to send and receive data to a PLC. the drive is simoreg 6ra70 I have 10 drive I want to have communicate to a PLC at the moment I only have 7 drive working. I have two drive between two other drive not working. Basically I got node 3 and 9 working, but node 5 and node 7 not working. I also change the drive with node 9 to node 7 to check if it was a PLC problem but it work on that drive. I also change the profibus card from one of the other drive that work to a drive that wasn’t working but it did not do anything. Then I installed the card back to it original drive, that drive also doesn’t work now. The red and gold/yellow LED lights are blinking in the profibus card on the drive that do not work.
Any suggestion???
Thanks for your help
"The red and gold/yellow LED lights are blinking in the profibus card on the drive that do not work."
Read the manual for what it means.
Check cabling and correct use of end resistors.
The timing of the lights flashing can give you an indication of what the problem is, I think it's described in the drive manual.
First check the cabling very thoroghly to ensure that all he cnnections are secure, the right way round (A and B not swapped) and that there is terminator a each end of the bus.
Second check that each slave has a unique address set (P918?) and verify that they are all seen on the bus by the master (If using S7, go online with hardware manager).
Once all are OK at the hardware level, tha only leaves your software.
Nick
Hi All, I am facing one issue with the SEW MDX61B drive. Issue- I want to run a conveyor with this drive in two directions but it runs in...
344
Hello, I'm trying to configure Profibus communications between a CPU1214c by module cm1243-5 and a Parker 590 DC drive. in tia poral software, hex...
1,121
Dear Sir, I have a healthy profibus communication between SIEMENS PLC S7 400 and Allen Bradley drive PF700 using 20-comm-p profibus dp module...
2,826
Experts! Need Help In My application i have Siemens CPU 316 WITH APPROX 28 PROFIBUS NODES (including Simovert Master Drive -14N.o.s & IM153 &...
4,876
Dear superiors, When i try to communicate Yasakawa A1000 AC Drive and simense s7-300 plc via profibus the drive shows error bb on its display...
6,898