Profibus with CLX

hcath

Member
Join Date
Feb 2012
Location
DE
Posts
3
Hi guys,

I am against the wall with a weird problem. CLX drives a series of Wago and SMC nodes thru Profibus, mostly digital I/O's. What happens is that periodically the outputs from nodes de-energize for a few seconds and then come right back on. At this time the PLC steadily sends ON request. It happens once every few hours without any particular pattern. All indications are that something happens in Profibus part. Has anyone had any similar stuff with Profibus? Would appreciate any advice
 
Hi guys,

I am against the wall with a weird problem. CLX drives a series of Wago and SMC nodes thru Profibus, mostly digital I/O's. What happens is that periodically the outputs from nodes de-energize for a few seconds and then come right back on. At this time the PLC steadily sends ON request. It happens once every few hours without any particular pattern. All indications are that something happens in Profibus part. Has anyone had any similar stuff with Profibus? Would appreciate any advice

Make sure the wago are held properly. Remove and fix back firmly. Does it happen with random mondules or same module. If same module try and replace
 
I had the same situation before, I have SST Scanner, wago modules, festo and smc penumatics then linear encoder.

the reason was loose wiring on the m12 connector (linear encoder) and also 1 time on festo module, the electronic chip (addressing) giving time to time error.
 

Similar Topics

Hi experts! Is there a compatibility of firmware version between PLC L72s and SST-PB3-CLX-RLL profibus scanner ? I upgraded my PLC firmware from...
Replies
0
Views
1,225
Hi, I've a 1756-L82E and need to manage some Profibus/DP peripherals (ET200M and 1794-APB) I was considering "in-chassis" solutions: - Prosoft...
Replies
4
Views
1,913
Hello Everyone, Have some cards Profibus SST-PB3-CLX Card that after power down, when back online again just said EB14 error. Anyone know this...
Replies
0
Views
2,150
Hi guys, I am in need of some advice from people with experience with the above. I am currently replacing a client's SST-PFB-CLX profibus...
Replies
1
Views
6,433
Hi, guys, how’s going? We have one production line that uses AB logix5000 as main PLC and FANUC robot, SIEMENS 840Dpl as slaves. The slaves...
Replies
1
Views
1,647
Back
Top Bottom