Programing a analogh module
Feb 2007
Oklahoma
277
Hi to all,
Our maintenance manager wants me to write a simple program using a MicroLogix 1500 plc with a Compact I/O Analog module 1769-IF4 SER A REV 2. What he wantsis for me to write a program that opens and closes a contact from a level gauge using a 4-20 mA input to the analog module. He wants the contact to open at 9mA and to close at 11mA. I think we are using 5v power for the sensor. I do not have experience with analog inputs. Could someone please give me an example of how I could write this program. I like to learn and this is a good opertunity. Thank you all very much.
See sample program below. Not knowing your system I put the analog card in the first slot yours may be different.
To see how the card is configured click on I/O configuration-highlight the card and click on Adv Config.
I would check on the 5 VDC Supply for your Sensor. It sounds too low for a 4-20 mA Device.
Stu....
9ma to 11ma control
Hi Mickey,
I just try the progamme you posted here about "9ma to 11ma control" issue. This programme is so wonderful that even I don't believe it can work well at first.It's so simple, but not easy to understand. I try several ways to make new programme. But I am not satisfied with my solutions. Then I think about the topics again,what kind of control do we really want here? Finally, I understand this is a typical one point control with Deadband setting. Then I reprogram this. It works well. However my answer is exactly similiar with yours.
I am very interested in this topics because this is a very normal topics in the automation control area. We have a built-in PID in ML1400. But for one ponit and two ponit controls, we need to program them by ourself. You make this programme neat and efficient. Looks like you are a professional programmer.
I posted some questions here before. Some I still didn't get a good answer, such as how to debug ML1400 offline and online.Hope you can review my post and give me some advice.
Thanks in advance.
Hi Mickey,
Thanks in advance.
I posted this on one of your other threads. After reviewing the offline program several times.
IMHO the only way to debug a program is to connect all inputs and outputs do a loop verification for all I/O ( test them all). Power up your system, make sure you know where the emergency stop is and make sure all personal are at a safe distance. Also have a fire extinguisher close by. Then put the processsor in the run mode and watch what happens.
Hi Mickey,
I appreciate your help, but I do not have winzip on my computer. Is there another way you could let me see the program? I have been around RsLogix 500 software, but have not done any programs using analog modules for the Slic500 or MicroLogix 1500 because the need never was there until now. I would like to learn more about using analog modules on programs. Is there a place on line where I could learn more about them? Thank you very much for your help.
I am new to analog programming and was wondering if I:1.0 means the .0 is for channe zero? If I wanted to add another analog 4-20mA input to control another sensor ,whould it be programmed as I:1.1? Sorry for the simple question, I just want to learn how to use analog module(s) on the MicroLogix 1500 PLC. I know that the MicroLogix uses inputs as I:0/0, I:0/1 etc. so the analog card added to it would be I:1.0, I:1.1, I:1.2 etc. depending on the card and scale used? :)
H
For the MicroLogix 1500 to reconize the add on analog module for programing it, how do I confuger it in RsLogix 500 softwer so I can write a program where it reconizes the new inputs? Thank you all.
Click on I/O configuration-Find your module and click on it-Then highlight it and click on "Adv Config"-then configure the module as desired-click Apply/ok. See Picture below.
Hello, I have Guard PLC 1600 by Rockwell Automation (it has been obsolete by them but still in the market and works fine). I need know if this...
1,224
I got DL06 AutomationDirect PLC to program with DirectSOFT6. It is a simple machine (40 in and 20 out, all digital), few valves, a simple conveyor...
23
6,891
Please suggest me programing cable for omron plc sysmac model no. Cpm2a
1,130
hi all, I am a PLC beginner.trying to learn how to program on my own at home. I am about to purchase a training kit online and just needed some...
17
5,185
please suguest me the cable names of following urgent 1) programming cable for PLC nexgenie 2000 model 2) PLC nexgenie 1000 model NG16DL
1,318