Programing the analog inputs on ml1100
uetm
Jan 2012
NASHUA NH
I am using the AB ML1100 PLC's analog inputs for set point control of a pump for both automatic pumping down a vacuum tank and pumping up of a Pressure tank. I have a vacuum sensor with a (-30 to 0 "hg) 4 - 20 ma output and a pressure sensor with(0 to 100 psi) a 4 - 20 ma output as inputs to v1 and v2.
I plan to have the vacuum setpoints as -22 "Hg to 15"Hg and the pressure setpoints as 25 psi to 60 psi.
My question is how do I program instructions I:0.4 and I:0.5 to accomplish the above?
I would appreciate any suggestions.
Harold Solomon
Harold,
You will also need to modify the wiring if you plan to use the 4-20mA transmitters. The ML1100 only supports 0-10V on the 2 x base analogues. If you wire a 500ohm (precision) resistor across IN0+ and ANL COM (for the first transmitter), you should get (approx) 2-10V deflection.
Just use an SCP instruction to scale your data - see pic below as a typical example...
Hope this helps get you started.
Regards,
Rob
dear All. I have one module analog 1769-IF4. I read manual, I saw every chanel ( CH0-->CH3) it have 1 word for configuration operation. such as...
5,242
Anyone know how to program a AB Pico 1760-18-lbwb-ex analog input's to be compared against a constant ? Any links etc would be greatly appreciated
1,761
hi, I am new to PLC programming. now i am doing a mini project using PLC to control the temperature of liquid.I have RTD and it's signal...
4,725
Hello, I have Guard PLC 1600 by Rockwell Automation (it has been obsolete by them but still in the market and works fine). I need know if this...
1,223
I got DL06 AutomationDirect PLC to program with DirectSOFT6. It is a simple machine (40 in and 20 out, all digital), few valves, a simple conveyor...
23
6,889