ckchew666 Member Join Date Aug 2003 Location Malaysia Posts 591 May 4, 2005 #1 Hi, Does anyone know if we can put a Prosoft Modbus module in the ControlLogix redundant CPU Chassis each? Will it cause any negative effect to the system? Thx.
Hi, Does anyone know if we can put a Prosoft Modbus module in the ControlLogix redundant CPU Chassis each? Will it cause any negative effect to the system? Thx.
Contr_Conn Member Join Date Sep 2003 Location Ohio Posts 2,576 May 4, 2005 #2 Look at the redundancy manual: it clearly stated what modules can be put in redundancy racks. Prosoft module is not on the list. But you can put it in remote (I/O) chasis.
Look at the redundancy manual: it clearly stated what modules can be put in redundancy racks. Prosoft module is not on the list. But you can put it in remote (I/O) chasis.
ckchew666 Member OP Join Date Aug 2003 Location Malaysia Posts 591 May 6, 2005 #3 Contr_Conn said: Look at the redundancy manual: it clearly stated what modules can be put in redundancy racks. Prosoft module is not on the list. But you can put it in remote (I/O) chasis. Click to expand... Thx a lot.
Contr_Conn said: Look at the redundancy manual: it clearly stated what modules can be put in redundancy racks. Prosoft module is not on the list. But you can put it in remote (I/O) chasis. Click to expand... Thx a lot.