Purpose of duplicate contact in series on a single rung
CalG
Feb 2013
VT
197
I have pulled the Ladder listing from the GE 90/30 without any other documentation.
Viewing the ladder print out, I see several instances where the same contact is used in series with no vertical wires between.
I have this rung (actually rung 48 in a MANUAL Block)
-]1[------]2[----]3[---]4[----]5[---]4[-----------------------<+>
<+>------]6[----]7[---]8[--------]etc[------------------------------( )
All the contacts are NO, with contact 4, an %I0006 (vacuum sense bellows), used twice in series on this one rung.
Is this for a purpose? Redundancy? Or legacy of some earlier edit?
Inquiring minds....
TIA
Cal
Hi
Earlier GE 90-30 low end CPU's did not allow online edits but you could overtype the instruction so some people (me included) would adopt a double contact to either reserve a contact or to remove a contact...
Although I would use %S7 Always on
I think cjd1965 has the correct explanation. The CPU311 does not allow editing a rung without stopping the PLC, but it does allow you to replace one address with another while running. Probably someone monitoring the rung during startup realized he didn't want what was originally programmed at one of the instances of %I0006 and replaced it with a second instance of %I0006. His intent would probably have been clearer if he had replaced the contact he didn't want with %S0007 (ALW_ON).
Hello everyone, I'm relatively new to PLCs and currently engaged in an R&D project involving multiple sensors for measuring torque, RPM, and...
164
We finally replaced our Cognex Checker with an IV-3 and I'm wondering if can replace the s/w in the monitor with anything else. I haven't been...
105
Hello everyone. I am currently doing a project to teach about ethernet topologies such as ring or bus. For example. But instead of using an...
4,349
Hello Friends, I want to learn Delta-v DCS, I'm looking for Delta-v DCS programming software (Demo or in VM Ware) Please. I'll be grateful...
1,687
Hi Guys, I am aware that the S7-1200 series on their right side have an I/O expansion port. Like this...
1,572