PV 300 connected to a micrologix 1200 using DF1
pcalonzi2
Jul 2008
Crawfordsville IN
Hi everyone,
I have a DF1 PV300 (AB p/n: 2711-K3A17L1) connected to a Micrologix 1200 (AB p/n: 1762-L24BXBR) using cable 2711-NC21. I am using 1761-CBL-PM02. I can see the plc in rslogix (using the RS232 DF1 driver). However I do not see the panelview. Do I need to enable the DF1 pass through or do I have the wrong cable? Also, this is a brand new panelview so it defaults to the configuration mode screen and alarms with Error 1110 becuase there is no program existing on the unit.
Please let me know what to do to get this going.
Thank you,
-Pat
Your ML1200 does not support passthru. And yes you will need to load a program in your PV. Do have PanelBuilder32 software for programming your PV? Cable is correct ( straight thru cable)
pcalonzi2 said:
Yes I have panelbuilder32. How can I setup the panelview to communicate with the plc and my laptop all at the same time?
-Pat
You cannot do it at the same time.
Program your ML1200. Make a note of how the HMI/Program port is configured. Then make sure your PV's port is configured the same.
See pics below for an example.
I saw that and was figuring that was the case. However, this knowledgebase article hints at being able to do it with a pv550 and a ml1200. My plc has the second comm port.
-Pat
Ok. As the KB says, if you want to see both ML1200 and your PV at the same time you will need the port splitter or a PV with DH485 protocol.
Just having the second port on your ML1200 does not do this for you.
pv550 help
hi mickey and all,,!
i have same problem,,,i have pv550 2711-b5a5, when i start it error 111o appears,,,and no valid application found,,
what should i do now?? i have pannel builder in my laptop but not serial port to communicate,,!
muds
Can you open the file with Panelbuilder32? If so save it as a *.PBA file and try to download it.
See pic for error message .
  • PVA_to_PBA.pdf
pv550 help
thanks for ur reply,,!
one more questin is that
i am little confuse ,,that 1747-uic serial port attached to pv550 is male and same male port with pv550,,
so how i attached directly 1747-uic serial cable to pv550?
should i need male to femlae convertor? or any other way??
thanks mickey ,,,that is really helpful,,
and mickey can u give me steps to interface pannel builder and to upload programme on my computer,,,?
and also what if i use serial port of my old PC instead of going of 1747-uic and 2711-nc13? waht should i do require for this..!
With a real serial port on your PC you can use a straight thru cable and the 1747-PIC/AIC+ driver in RSLinx.
What operating system do you have in your PC?
If Windows XP SP3 there are issues when using this driver, there is a patch for it though. See link.
http://plctalk.net/qanda/showthread.php?t=63919
For uploading/downloading your program see chapter 11 of the manual below.
The memory card method for upload/download is always a good option.
http://literature.rockwellautomation.com/idc/groups/literature/documents/gr/2711-gr003_-en-p.pdf
hi mickey n all
straight through cable means
Female DB-9 Female DB-9
Connector Connector
DCD 1 -------------- 1 DCD
TXD 2 -------------- 2 RXD
RXD 3 -------------- 3 TXD
DTR 4 -------------- 4 DTR
COM 5 -------------- 5 COM
DSR 6 6 DSR
RTS 7 -------------- 7 RTS
CTS 8 -------------- 8 CTS
9 9
m i right?
n thanks for your supporting documents,!
hi mickey n all
Connector Connector
DSR 6 6 DSR
9 9
m i right?
See pdf
Dear Friends; We have a BOBST 1228 flexo printing machine having Siemens S7-300 PLC (6ES7 318-3EL01-0AB0) and Lenze 9300 and 9400 drives. The...
2,317
hi there its my firest time working with profibus and i have already install gsd and networked profibus in step7 hw config and inserted base...
2,515
This is one for the siemens crowd. We want to replace a S5 95U connected to 3 banks of I/O I am not kidding when I say lots of I/O. All I/O are 8...
3,115
Error 612 no active nodes found on network. I'm using an Allen Bradley 1761-CBL-PM02 SER C cable. I downloaded the program to the PLC and to the...
4,636
Replacement of variator Danfoss "VLT 5000" "FC 300"connected to S7 300 "PROFIBUS" Hello, I must replace the variator VLT 5000 by FC 300...
3,389