PV550 to 1761-NET-AIC

Join Date
Mar 2005
Posts
49
I have a panelview 550(2711 k5a5) connected with a 2711-NC21 cable to a 1761-NET-AIC, ML1500 LRP connected with a 1761-cbl-hm02 cable to a 1761-NET-AIC.

I can see the Micrologix in RSlinx but I can't see the Panveiw...The node for my computer is 00, ML is 01 and the Panview is 02.

Everthing is set up for 19.2k, different node numbers.

Am I missing something regarding the Panveiw 550? or DH 485?

The communication setup in the 550 only lets u configure the max node(31), node(2) and the baud(19.2k).

Don't really have alot of options when it comes to trouble shootin. I have have me network terminated at either end and the grounded on one side.
 
"The node for my computer is 00, ML is 01 and the Panview is 02."

You can connect computer to NET-AIC and view both ML1500 and panel view. Did you try doing that???
 
Thats what I am doing....I have my computer connected to the DB9 the ML1500 connected the 8mini the two AIC connected together and the panelview 550 connected to the 8mini on the other AIC...
 
I think the problem might be the NC21 cable, it is designed for the PV300. I think you need the NC13 for your PV. See attached
 
Correction on my previous post, about the NC21 and NC13 cables see attached. Sorry if I misled you but I'm also confused now.
 
The panelview 550 is running 485 through it's re 232 port.

I know this because I connected directly to the MicroLogi 1500 and reconfigured it's port for DH 485, and it established comm.

That is fine, but i wasn't planning on directly connecting the two. I need to go through a 1761-NET-AIC.

I am trying to figure out where I went wrong....I can find lots of documents showing a Panelview 550 RS 232(DH 485) connected to a NET-AIC.

Does anyone know what I have to do to get this to work? Reconfigure the port for DF1?????
 
Alright, I am online.....The 2711 NC21 is the right cable series A revision B.

Rookie DH 485 misktake.....I was using the DF1 driver.

I switched it to the PIC driver and I configured the comm port on the PLC to DH 485 and I can see both in RSLinx...

Thanks for ur help
 

Similar Topics

Is there a way to add a stop to the attached program? I want to stop it after the first rinse so the operator would have to push a button for it...
Replies
10
Views
1,229
I'm trying to connect a PV550 (2711-T5A2L) to a 1761-NET-AIC using a 1747-C11 cable (w/RJ45 removed) and the Phoenix connector. Can someone tell...
Replies
8
Views
2,672
We have an old machine that has been mothballed since early 2018 and management are looking at more work for it in 2022. The system runs on an SLC...
Replies
12
Views
2,881
Trying to write a program for a PV550 (2711-T5A16L1, Ser. B, Rev. E, FRN 4.46) to test the touchscreen. I wrote a program with 16 pages and on...
Replies
2
Views
1,696
Good Morning Folks. Win Xp, PRO, Version 2002, SP3 RSLinx Classic 2.54 Using the AB UIC-485 driver with the 1747-UIC and a 2711-NC13 connected...
Replies
1
Views
1,223
Back
Top Bottom