Question about Product Spec Output Relay
tranh2
Jul 2009
Ontario
40
Hello,
I have a question about a product in general. I'm looking at a Carbon Monoxide detector product datasheet. In it it says that is has
Optional Relay:
Outputs - Form C contacts (NO and NC), 5 Amps @ 250 Vac, 5 Amps @ 30 Vdc.
Does this mean when actuated it outputs 5 Amps @ 250 Vac or 5 Amps @ 30 Vdc from that contact? So if i place a multimeter on those contact thats what I would see on my multimeter? So I would wire from these contacts directly to the power input of the device that can handle those power ratings?
Or is that the max load rating those contacts can handle? i'm new to this electrical design part.
Thank you!
Key word OPTIONAL
it may not have a relay at all if it wasn't ordered with one
it only stated the if the optional relay is there the 5 amp at 250 VAC or 5 amps at 30 VDC
No
Yes
Yes it's the max, resistive unless stated otherwise, load. Best to stay well below that maximum to extend the contact life. And you might also need to take additional measures to protect the contacts too depending on exactly what you're switching and how much the detector costs.
Hey guys,
Thanks for the replies. I'm a little more clear but unclear on some parts. I've sketched two configurations. I'm trying to put together a CO detector that drives a siren.
I'd like to use the Honeywell E3Point model. It comes with two output relays rated at 2 DPDT relays, 5A @ 250Vac; 5A @ 30Vdc.
http://www.honeywellanalytics.com/~/media/honeywell-
analytics/products/e3point/documents/e3point-quick-start-guide.pdf?la=en
For the siren i'm using the Federal Signal LP4 rated at Voltage: 9-28VDC.
https://www.fedsig.com/resource-document/file/9233
For the 24VDC i'm just using a simple Phoenix Contact 24VDC PS with MAX output of 10A. Nothing special.
If I understand Configuration2 should be the correct way to wire it up?
Hey guys,
Number 2
If it were me, I'd use an interposing relay between the CO detector and siren.
The relays built into instruments are usually not replaceable, whereas an interposing relay is $20, pull-out/plug-in. It's a $20 insurance policy.
Is it possible to weigh parts during the pick and place process? The part I am interested in weighing are between 100g and 400g. Is there a scale...
3,183
I have a 120V relay, 120V DI card and a analog input. I was wanting to know if i could put a 24V DI and well as a 120V DI card on the same plc...
60
Hello again..trying something on an existing poorly written program and just wanted to double check something system is an A-B MicroLogix 1200 In...
184
Good morning! Let me start by saying, I am still learning about this type of HMI programming. I recently watched a video about recipes and how it...
161
I have some logic that I have written within a 5380 series controller that tracks the time an event is started, while the event is running an RTO...
102