question about S7-GRaph

userxyz

Member
Join Date
May 2002
Location
any
Posts
2,768
Hi all,

As you know there is a S_NO Output parameter after compiling.

You can connect an integer to it so that you can monitor the actual stepnumber on an HMI device for example.

But, when you have parallel sequences, S_NO allways shows the last step that is active, parallel steps cannot be shown ??

The question is: How can I show ALL active steps. I use ProAgent for my new project, and it works fine. But my collegue wants to keep his current project without proagent and wants to be able to show parallel steps in I/O fiels of an HMI device.

Thanks in forward.

Kind Regards,

Gerry
 
Because you have parallel process I would not use Step Number. I would monitor active Steps via Instance DB or because of my style I would setup status Flags for each Step which I can monitor. Easier to understand and I can call them anything I want in the STAT area and monitor them in the HMI with a little diagram to mimics my Graph program.


Nick
 

Similar Topics

Hello, What are Permanent pre-instructions and Permanent post-instructions that you can program in the Tia Graph FB's ? Thanks, kind regards, G
Replies
5
Views
1,781
As i am newbie in S7 Graph, could anyone please explain me what is doing monitoring function in S7 graph.What is supervision line and required...
Replies
0
Views
1,878
I have a problem with Lenze positioning via the AIF interface. I control the 15 ECS drives (application version 1.3) with a 317 Siemens CPU on a...
Replies
4
Views
1,787
I have a 120V relay, 120V DI card and a analog input. I was wanting to know if i could put a 24V DI and well as a 120V DI card on the same plc...
Replies
1
Views
67
Hello again..trying something on an existing poorly written program and just wanted to double check something system is an A-B MicroLogix 1200 In...
Replies
5
Views
185
Back
Top Bottom